What are formula we can apply to determine the HT/LT current of 11KV/433V transformer except KVA/LV×√3. ?
Answers were Sorted based on User's Feedback
Fourmela No 1 power in one phase/Voltage in one phase(I.e phase voltage)
example there is a 300 KVA 11KV/433 V transfomula. Power in one phase 300KVA/3 =100KVA both in HT & LT side, Phase voltase in HT side 11/√3 = 6351Volt .Phase voltage in LT side 433/√3 = 250 Volt.
According to formula HT side current 100,000/6351 = 15. 7 amps. and LT side current 100,000/250 = 400 amps
Formula No 2 for HT side transformer in kVA/20 and for LT side KVA×4/3. field lineman are using this formula.
According to this formula 300 KVA transformer's HT side current 300/20 =15 amps apporximately +5℅ may added for big size to accurate value. And LT side current 300×4/3 = 400 amps apprx.
In general formula for 300 KVA 11KV/433V transformer HT side current KVA/LV×√3 i.e 300000/11000×1.732 = 15.7 amps .LT side current 300000/433×√3 = 400 amps
PRADYUMNA CHANDRA PANDA
mob No 943
7917849
Is This Answer Correct ? | 4 Yes | 6 No |
Answer / haider
P=Root3 *VIcos$
P=KVA rating of DTR
V=primary volage (HV side)
cos$=power factor
Exp:
100KVA DTR
primary volage =11000V
let Power factor=0.97
I=kva/1.732*11000*0.97
I=5A
Is This Answer Correct ? | 12 Yes | 18 No |
Wtat is vaccum currcuit breaker.define with cause of used.and where be use it Devise .
Before given the connection to Alternator (pre- commissioning) which tests we will conduct
What is meant by load angle of an alternator? Upon what factors does the load angle depend?
Why L.T.Cable voltage rating is 1.1kV,where as system voltage is 0.415kV?
What is the meager?
why we connect dg neutral with ground?
how many minutes or seconds taken by the transmission of electrical power from generating end to distributing end?
why transformer are not used in D.C SUPPLY
what is the difference between STAR and DELTA connection and application wise how it can be utilizedd
ALONG WITH MEGGER TEST FOR CHECKING OF MOTOR ,WHY WE MEASURE FOR RESISTANCE AND INDUCTANCE?
why air handling unit interloking in case of fire
what are the components of a start and stop motor control?