What are formula we can apply to determine the HT/LT current of 11KV/433V transformer except KVA/LV×√3. ?
Answers were Sorted based on User's Feedback
Fourmela No 1 power in one phase/Voltage in one phase(I.e phase voltage)
example there is a 300 KVA 11KV/433 V transfomula. Power in one phase 300KVA/3 =100KVA both in HT & LT side, Phase voltase in HT side 11/√3 = 6351Volt .Phase voltage in LT side 433/√3 = 250 Volt.
According to formula HT side current 100,000/6351 = 15. 7 amps. and LT side current 100,000/250 = 400 amps
Formula No 2 for HT side transformer in kVA/20 and for LT side KVA×4/3. field lineman are using this formula.
According to this formula 300 KVA transformer's HT side current 300/20 =15 amps apporximately +5℅ may added for big size to accurate value. And LT side current 300×4/3 = 400 amps apprx.
In general formula for 300 KVA 11KV/433V transformer HT side current KVA/LV×√3 i.e 300000/11000×1.732 = 15.7 amps .LT side current 300000/433×√3 = 400 amps
PRADYUMNA CHANDRA PANDA
mob No 943
7917849
| Is This Answer Correct ? | 4 Yes | 6 No |
Answer / haider
P=Root3 *VIcos$
P=KVA rating of DTR
V=primary volage (HV side)
cos$=power factor
Exp:
100KVA DTR
primary volage =11000V
let Power factor=0.97
I=kva/1.732*11000*0.97
I=5A
| Is This Answer Correct ? | 12 Yes | 18 No |
what are the parameters plays a major role in Potential transformer Burden calculation??
sir& friends i want the collection of recent quetions asked in interview of top most companies please send me on my email san.jsr@hotmail.com
what & how to check the lightning arrester
In single phase ac ups supply when current is measured with tong tester neutral current is found more than phase current.What is the reason?
what is power factor when in view of a lineman
why the capacitor bank unit is kvar
why we do not get the electric shock at end of returning water of water cooled cable
How to calculate the sag on transmission Lines.
calculate multiplication factor of a trivector meter with line ct ratio 200/5A, line PT ratio 11000/110V and meter CT ratio 200/1A and meter pt Ratio 11000/110V.
which of the folowing has negative temperature coefficient of resistance? a. mercury b. copper c. lead d. carbon
The unit of resistivity is:(a) ohms(b) ohm millimetre(c) ohm metre(d) ohm/metre
What is technical difference between ELCB & ELMCB?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)