how will i find Transformer rating if supply voltage is
11k.v and how will i find incomer if transformer rating is
12MVA
Answers were Sorted based on User's Feedback
Answer / subhash sapkal
12MVA Tranformer connect in 11KV linne . 1>primery side
curret is =< 1090A
2> same trasformer in 33KV primery current is =< 363A
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / koraim
you have to know two parameter out of these (Power ,
voltage & Current) as a basic then you can get whatever u
want.
if the transformer is 12 MVA and 11 kV and assuming that it
is 3 phase, then the current is 630
| Is This Answer Correct ? | 2 Yes | 0 No |
What is kirchoff ’s current law (kcl)?
What will happen if DC supply is given on the primary of a transformer?
if our load is 65000 watts howcan we find out all char like cable size. mcccb etc
generally in LT and MV motors we are using 3.5Coresx16,25,35,50 etc cable for supply.although motors is earthed at two point and having all protection.then why we are using that 1/2 core for earthing the motors.while in HT cable we are using only 3core cable for motor supply.generally lt and mv motors are delta connected and ht motors having star connection.whethere it is having any relation with winding connection( star or delta).all motors i am talking about are dol only.can anybody solve my confusion.thanks...
how we can adjust for three phase motor cold stall time ,hot stall time and thermal register set up?
my name is venkat .i have good percentage in my academics(ssc 86, intermediate 83 b.tech 73) my question 1..after completion of my ssc i joined in bpc but i didnt got rank in emcet so i completed MPC in one year compartmentally ..so here what am expect question from this background?
in an open circuit. test there is no load curent.. but secondary. ia open then no urrent have to flow but there a smaller current flows why?
Why the motor was take the starting current is high?
what is kvarh? Please difine it With calculation
How to calculate earth flat size for 250 Kva DG and transformer?
How to select Main CB Rating for 220 KW Load?
how to mention 5mw generator in kva ? gen voltage is 11kv
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)