how will i find Transformer rating if supply voltage is
11k.v and how will i find incomer if transformer rating is
12MVA
Answers were Sorted based on User's Feedback
Answer / subhash sapkal
12MVA Tranformer connect in 11KV linne . 1>primery side
curret is =< 1090A
2> same trasformer in 33KV primery current is =< 363A
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / koraim
you have to know two parameter out of these (Power ,
voltage & Current) as a basic then you can get whatever u
want.
if the transformer is 12 MVA and 11 kV and assuming that it
is 3 phase, then the current is 630
Is This Answer Correct ? | 2 Yes | 0 No |