Answer / attique330
meager is instrument which is used to measurement of high
resistance of insulation and quality.
| Is This Answer Correct ? | 38 Yes | 5 No |
Answer / rajesh upadhyay
megger used for any winding insulation resistance
mesurement.
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / pradyumna chandra panda
Meager(Insulation Tester) is used for measer high value of resistance such mega ohm, gega ohm, tera ohm which offer in between cable core , winding and body etc. NB. Some time we wrongly say that value a apparatus or a cable is infinative maga ohm. Actualy there is a vaule of Mega , gega or ,tera which is determine by using high range of meager of high voltage.
| Is This Answer Correct ? | 8 Yes | 1 No |
Most likely the misspelled "Megger". Megger is a company whose Insulation Resistance meter is so well known; people usually associates any insulation resistance meter as 'megger tester'.
| Is This Answer Correct ? | 10 Yes | 8 No |
Answer / guest
megar is nothing but to check the IR value of the cable .and
also use for cable fault find
| Is This Answer Correct ? | 3 Yes | 2 No |
How can calculate the rating of a servo stabilizer for given a specific load
15 kva dg set single phase takes 63amp( approximate) while same rating 15kva three phase takes 35amp approximate. why ? and what will be per phase current for 15 kva
In UPS, battery connections if parallel connection given, what will happen?
How the annunciator works ? How to do its wiring
howmuch current can carry the 2.5Sqmm copper cable?
Is there thumb rule to calculate how many Insulators to be used for Transmission line of different volatges
WHAT WILL HAPPEN IF WE START A MOTOR WITH STAR & IT IS RUNNING WITH STAR CONNECTION INSTEAD OF DELTA
why effective resistance should be more than static resistance in transmission line?
in 132 kv substation ligtning arrestor(120 kv) connected to line. but line voltage comes to 132 kv, it operate or not???
12.5 tons a/c is their how much kva generator can recommend to the customer.
why the power factor in inductive load is lagging while it is leading in capacitive load?
why core losses are affected with change in voltege in transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)