1 ton AC takes how much current( starting & stable)
Answers were Sorted based on User's Feedback
Answer / bk mishra
A 1 ton Air conditioner is appx 1400 watts . so
1400/230=7.8 Amp is the runing current.
| Is This Answer Correct ? | 107 Yes | 82 No |
Answer / aks
Mr Answer is correct. As a thumb rule we choose breaker of 2 - 2.5 times of rated current.
| Is This Answer Correct ? | 42 Yes | 18 No |
Answer / sanjay singh
there is difference between running current and starting current.can anybody answer what is the starting current for 1.5 ton 3 star ac
| Is This Answer Correct ? | 24 Yes | 6 No |
Answer / bala_vlsi
Mr. Mishra as perr you calculation 7.8 A then why all the
people are recommended 15 /20 A BEREAKER for the above load
| Is This Answer Correct ? | 30 Yes | 14 No |
Answer / abhay sisodia
1 Tonn of refrigeration consumes 1400 watt approx. For
coverting watt to ampere we have to divide 1400 to 230volt
it comes approx 6amperes for safety meausres we select 3
times bigger MCB that means 18ampere.
| Is This Answer Correct ? | 16 Yes | 10 No |
Answer / rajesh
Checked the Current of LG 1 Ton AC with Clamp Meter Stable Current is 0.3 Amps and When Compressor is On it is 4.78Amps RMS
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / tony
All the answers are actually wrong. MCBs can handle quite a larger current (2-15 times, depending on type) for short period of time so you don't consider inrush current.
Type B: 3-5 times
Type C: 5-10 times
Type D: 10-20 times
The breaker in the distribution box usually is dependent wire gauges. You can adjust the mcb with socket according to load.
Use type C for ac. Only use 1.5 times of the running current. I use 13A for 1.5 ton ac.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / qaiser shah
well i ve 1 ton LG Window AC, i ve checked its running amperage is 6.23A, So my answer is 6-7A in running , i ve connected a breaker of 10A which does not trip on starting or running... i dont know the starting current...but i think may be 9A?
| Is This Answer Correct ? | 10 Yes | 8 No |
Answer / amartaya
32 A i MCB s perhaps wrong because if B type it can hold up to 95 A to 140 A for o0.05 seconds approx and for C type it can hold 150 to 300 A approx for 0.1 seconds . 16 A C type MCB will be enough.Thanks .
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / tech mech
Check the Specification sheet of the Air-conditioner for wattage consumed or running current in Amperes. Starting current for compressor motors can be safely assumed as 3.5 times the running current. MCB (breaker) rating should be 1.5 times the max current required that is the starting current. So, Breaker rating should be 5-6 times Aircon running current. This is unique to appliances with motors like Refrigerators, Air conditioners, Washing machines, water pumps etc.,
| Is This Answer Correct ? | 2 Yes | 4 No |
What are effect of radio system in DCS Distributed control system ?
what is smartµ grid technology?under coal gassification?
How do I know if a transformer is saturated? I am doing the simulation of the saturation of a transformer, but what parameter tells me when a transformer is saturated? How do you calculate? is on the plate?, there is a rule that can help me? How could model? I understand the saturation occurs when the flow can no longer bind to the other winding, this is given to certain current, this current is the same that appears as the highest in the bale of features? Thank you for your help Eduardo Alvarez Guatemala
what are the principles of a booster converter?
Draw the wave shape of armature current in a generator subjected to a sudden three phase short- circuit at its terminals. Define various reactance of generator from this wave shape.
what happens when one of the phases out 0f 3 phases been removed under working condition and no load condition will the machine run if so plz send me why
DEAR ALL I have motors ( 10 units )each one is 90kw 380V 50 HZ 1000rpm but new local pwer is 220v 60 hz requierd rpm should be 1000 pleas what the beast solution is used frequncy converter or rewinding all motos or chang all motors thanks
How can I calculate the trnaformer effciency at different loading condition?
Why earthing is required for diesel tank?
why hv winding is not placed near to transformer core
what are 3 factors when selecting a contactor for a job?
If we have use two power cable for incomer, that time how many use cbct for earth leakage protection? 1 or 2 if 1 way? If 2 way?
0 Answers REM Electromech Pvt Ltd,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)