some meggers have three terminals. wat is the real function of
the earth terminal?
Answers were Sorted based on User's Feedback
Answer / amit
THREE TERMINALS OF MEGGERS ARE = GROUND, EARTH, LINE
THREE TERMINAL USE = GROUND & LINE USE FOR CHECKING
RESISTANCE BETWEEN GROUND AND LINE
EARTH AND LINE ARE USE FOR CHECKING RESISTANCE BETWEEN TWO
TERMINALS ONE WINDING
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / baljeetsingh
meggers have only two terminals and three terminal device
mentioned by u is earth resistance tester.
meggers are used to check insulation value of any equipment
wrt earth which should be highest possible in m ohms and
earth resistance are used to check the effectiveness of
earth pits and their resistancce which should be lowest
possible in ohms
| Is This Answer Correct ? | 2 Yes | 1 No |
working principle of oil startar
What is the value of nuetral current in star connected load when DC is supplied to it???
in case of OC+EF relay, how the burden is divided/calculated/shared by the CTs in case of normal (healthy condition) and during fault conditions.? three coils of OC & ef coil is conected in residual connection across the three CTS.
on what factor insulation resistance depends
what is power factor?
what is pole slip ?
if in 3-phase system voltage=440V,frequency=60Hz, current=400A. then if it is single phase then current=? and if it is single phasing then current=?
a)In a 3-phase 4-wire circuit, a circuit breaker is selected to protect the circuit whose highest fault level is 6.6 MVA. Determine the required minimum breaking capacity in kA. (Note: Covert 3-phase power in terms of kA to find answer.) b)Using the below, determine the required minimum making capacity in kA as a “peak value”. Rate breaking capacity (Icn) ka: Icn<= 1.5 Factor = 1.41 1.5
What are the circuit models used for analysis of medium length transmission lines? Which one is superior? Support your answer.
our company have 750 kva oil transformer.still we have facing a problem that is when voltage is 11.5 kv coming from HT side then LT-side voltage is 420v or above at tape 1.please give me best solution to decrease the voltage.
while buying 30 kva on line ups for 1 phase ouput, we ave to calculate the number of batteries for 2 hours back up? how to calculate the ah rating and number of batteries
if three phase supply is given to single phase transformer, what will happen?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)