Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


sir, plz tell me how much kvar capacitor required for 1000
amp or 500 Kw load ? what is the formula ?

Answers were Sorted based on User's Feedback



sir, plz tell me how much kvar capacitor required for 1000 amp or 500 Kw load ? what is the formul..

Answer / madhu253

Formula : KVAR = KW(tanĂ˜1-tanĂ˜2)

Is This Answer Correct ?    38 Yes 10 No

sir, plz tell me how much kvar capacitor required for 1000 amp or 500 Kw load ? what is the formul..

Answer / prakash veer singh

Dear Shovan
This is Prakash veer
According to madhu's formulas,

KVAR= KW* (tanQ1-tanQ2)

Q1 is intail power factor
Q2 is target power factor

Is This Answer Correct ?    21 Yes 5 No

sir, plz tell me how much kvar capacitor required for 1000 amp or 500 Kw load ? what is the formul..

Answer / arun

we need power factor value

Is This Answer Correct ?    14 Yes 4 No

sir, plz tell me how much kvar capacitor required for 1000 amp or 500 Kw load ? what is the formul..

Answer / santosh maske

Required data for calculation your demand KVAR

1.Existing P.F of Load (tanQ1)(0.92)
2.Required P.F (Improvement in P.F)-(tanQ2)(0.99)
3.Supply Voltage - for reference(Voltage variation if any)
4.Load in KW (exam- availabl with you i.e 500KW)

KVAR= KW(tanQ1-tanQ2)
KVAR= 500(tan0.92- tan0.99)
KVAR = 500(0.2890)
KVAR = 141.75 KVAR (@ 142KVAR)
if you want to calculate by amp need following data
efficiency of motor, required P.F, KW,maganatising current
of motor,formula find in Electrical Machine Engineering

Is This Answer Correct ?    10 Yes 2 No

sir, plz tell me how much kvar capacitor required for 1000 amp or 500 Kw load ? what is the formul..

Answer / elangkumanan

25 kvar = 32amps load taken
12.5 kvar =16amps load taken
l6.25 kvar =8amps load taken
3.125kvar =4amps load taken
1.0775kvar =2amps load taken


1000amps capacitor required to 500kvar

Is This Answer Correct ?    6 Yes 1 No

sir, plz tell me how much kvar capacitor required for 1000 amp or 500 Kw load ? what is the formul..

Answer / deepak

kVAR=kVA X sinphi
SO, sin phi=(1-cos sq phi) underroot.
SO POWER FACTOR IS REQUIRED.

Is This Answer Correct ?    7 Yes 3 No

sir, plz tell me how much kvar capacitor required for 1000 amp or 500 Kw load ? what is the formul..

Answer / shovan

Madhu pls explain what is tanphi1 and tanphi2????

Is This Answer Correct ?    5 Yes 1 No

sir, plz tell me how much kvar capacitor required for 1000 amp or 500 Kw load ? what is the formul..

Answer / malkit singh

250 Kvar Capacitor bank is required for 500Kw load
(i.e,625Kva).
This is because the capacitor rating for any load is equal
to 40% of Kva.
i.e, Capacitor required=40%x Kva Load

Is This Answer Correct ?    8 Yes 5 No

sir, plz tell me how much kvar capacitor required for 1000 amp or 500 Kw load ? what is the formul..

Answer / saleem iqbal

plz identify your systems existing power factor and
targeted power factor which u want to improve, then apply
this formula
KW X (Tan phi 1 - tan phi 2)

Is This Answer Correct ?    2 Yes 0 No

sir, plz tell me how much kvar capacitor required for 1000 amp or 500 Kw load ? what is the formul..

Answer / bijoy roy

Reactive power (KVAR) is increase due to run inductive load.as a result power factor is lagging. so have to use capacitive power to reduce this inductive or reactive load. generally we have to use 63% capacitive load to remove the reactive load.i.e.

active power=500KW
so 60% of this will be=(60*500/100) = 300 KVAR

so we have to use 300KVAr capacitive capacitor bank to remove this reactive power .

Is This Answer Correct ?    2 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

1.why are not using acb 33kv ht side? is there any problem 2.what is difference between acb,vcb,sf6 breackers? 3.what is the function of invertor and convertor in ups?

0 Answers   L&T,


How electrical power(MW)is varied OF an A.C Generator in response to varying steam input to a steam turbine ?

1 Answers   Hindalco,


how a vibration switch's high signal will going to trip the motor? can u explain with some examplesand wiring diagrams?

1 Answers   Bhel, Wartsila,


Why is a synchronous motor always star connected??

0 Answers   Bhushan Power Steel,


what is the function of conservater in transformer

3 Answers  


Define active filter?

0 Answers  


How to calculate loses in transformer of 160 KVA ?

0 Answers   IDV,


What would be the steps and parameters in case if a fault occurs in transmission line at a distance far from the generating station?

0 Answers  


HOW TO CALCULATE THE LOSSES OF CURRENT FOR LT CABLE JOINTING TO MOTOR SUPPLY.

2 Answers  


what is integrated ac contact circuit

0 Answers  


IN 500 KVA TRANSFORMER 11KV/415 VOLTS HOW TO CALCULATE THE HT CABLE SIZE AND LT CABLE SIZE FROM TRANSFORMER TO LT PANNEL. AND HOW MANY MAINSWITCHES OR MCBS WITH RATING ARE TO BE PROVIDED

2 Answers   BSF,


Welding machine

1 Answers   CEL,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)