sir, plz tell me how much kvar capacitor required for 1000
amp or 500 Kw load ? what is the formula ?
Answers were Sorted based on User's Feedback
Dear Shovan
This is Prakash veer
According to madhu's formulas,
KVAR= KW* (tanQ1-tanQ2)
Q1 is intail power factor
Q2 is target power factor
| Is This Answer Correct ? | 21 Yes | 5 No |
Answer / santosh maske
Required data for calculation your demand KVAR
1.Existing P.F of Load (tanQ1)(0.92)
2.Required P.F (Improvement in P.F)-(tanQ2)(0.99)
3.Supply Voltage - for reference(Voltage variation if any)
4.Load in KW (exam- availabl with you i.e 500KW)
KVAR= KW(tanQ1-tanQ2)
KVAR= 500(tan0.92- tan0.99)
KVAR = 500(0.2890)
KVAR = 141.75 KVAR (@ 142KVAR)
if you want to calculate by amp need following data
efficiency of motor, required P.F, KW,maganatising current
of motor,formula find in Electrical Machine Engineering
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / elangkumanan
25 kvar = 32amps load taken
12.5 kvar =16amps load taken
l6.25 kvar =8amps load taken
3.125kvar =4amps load taken
1.0775kvar =2amps load taken
1000amps capacitor required to 500kvar
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / deepak
kVAR=kVA X sinphi
SO, sin phi=(1-cos sq phi) underroot.
SO POWER FACTOR IS REQUIRED.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / shovan
Madhu pls explain what is tanphi1 and tanphi2????
| Is This Answer Correct ? | 5 Yes | 1 No |
250 Kvar Capacitor bank is required for 500Kw load
(i.e,625Kva).
This is because the capacitor rating for any load is equal
to 40% of Kva.
i.e, Capacitor required=40%x Kva Load
| Is This Answer Correct ? | 8 Yes | 5 No |
Answer / saleem iqbal
plz identify your systems existing power factor and
targeted power factor which u want to improve, then apply
this formula
KW X (Tan phi 1 - tan phi 2)
| Is This Answer Correct ? | 2 Yes | 0 No |
Reactive power (KVAR) is increase due to run inductive load.as a result power factor is lagging. so have to use capacitive power to reduce this inductive or reactive load. generally we have to use 63% capacitive load to remove the reactive load.i.e.
active power=500KW
so 60% of this will be=(60*500/100) = 300 KVAR
so we have to use 300KVAr capacitive capacitor bank to remove this reactive power .
| Is This Answer Correct ? | 2 Yes | 0 No |
why is the rating of transformer done in kva and not in kw.
What is surge impedence and surge loading....???
hai...... tis is Hemanth. jst now completed electrical engineering... i wanna to apper for ap tranco exam... plzz send me the previous q's paper link......thanx in advance.
Can we indroduce the principle of single phase induction mator to Transformer? i.e. by Producing rotating flux in the transformer.
i m electrical diploma holder i want to do plc $ Scada some body tell me which insitute is best for me near chandigarh
What is the GI Earth Flat Size recomended for 33KV 2000KVA Distribution Transformer
Why synchronous motor runs at a fixed speed? what is the name of that fixed speed?
Explain cmrr?
what is function and advantage of double delta winding in induction generator?
Can someone tell me how to calculate the size of a power cable? What are the factors involved in cable sizing?
In a flange coupling, the flange bolts are designed for
what is the use of breather in transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)