sir, plz tell me how much kvar capacitor required for 1000
amp or 500 Kw load ? what is the formula ?
Answers were Sorted based on User's Feedback
Dear Shovan
This is Prakash veer
According to madhu's formulas,
KVAR= KW* (tanQ1-tanQ2)
Q1 is intail power factor
Q2 is target power factor
Is This Answer Correct ? | 21 Yes | 5 No |
Answer / santosh maske
Required data for calculation your demand KVAR
1.Existing P.F of Load (tanQ1)(0.92)
2.Required P.F (Improvement in P.F)-(tanQ2)(0.99)
3.Supply Voltage - for reference(Voltage variation if any)
4.Load in KW (exam- availabl with you i.e 500KW)
KVAR= KW(tanQ1-tanQ2)
KVAR= 500(tan0.92- tan0.99)
KVAR = 500(0.2890)
KVAR = 141.75 KVAR (@ 142KVAR)
if you want to calculate by amp need following data
efficiency of motor, required P.F, KW,maganatising current
of motor,formula find in Electrical Machine Engineering
Is This Answer Correct ? | 10 Yes | 2 No |
Answer / elangkumanan
25 kvar = 32amps load taken
12.5 kvar =16amps load taken
l6.25 kvar =8amps load taken
3.125kvar =4amps load taken
1.0775kvar =2amps load taken
1000amps capacitor required to 500kvar
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / deepak
kVAR=kVA X sinphi
SO, sin phi=(1-cos sq phi) underroot.
SO POWER FACTOR IS REQUIRED.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / shovan
Madhu pls explain what is tanphi1 and tanphi2????
Is This Answer Correct ? | 5 Yes | 1 No |
250 Kvar Capacitor bank is required for 500Kw load
(i.e,625Kva).
This is because the capacitor rating for any load is equal
to 40% of Kva.
i.e, Capacitor required=40%x Kva Load
Is This Answer Correct ? | 8 Yes | 5 No |
Answer / saleem iqbal
plz identify your systems existing power factor and
targeted power factor which u want to improve, then apply
this formula
KW X (Tan phi 1 - tan phi 2)
Is This Answer Correct ? | 2 Yes | 0 No |
Reactive power (KVAR) is increase due to run inductive load.as a result power factor is lagging. so have to use capacitive power to reduce this inductive or reactive load. generally we have to use 63% capacitive load to remove the reactive load.i.e.
active power=500KW
so 60% of this will be=(60*500/100) = 300 KVAR
so we have to use 300KVAr capacitive capacitor bank to remove this reactive power .
Is This Answer Correct ? | 2 Yes | 0 No |
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
what is the difference between the alternator used in hydro and thermal power plants??
What is ferrite affects and what is disadvantage of ferrite affects.
1.what is the funtion of chiller primary & scondary pumps. 2.what is the use of distribution lines & Types. 3.what is the use the thermal power stations & how much capacity.
How can I communicate with an Areva MiCOM P121 relay by RS485 port? In other word, which command can I send and what information can I have recieved? please send some refrences, please. thanks
what is neutral ground resistance relay? how it is helpful in protecting system?
what are the different methods for the starting of a synchronous motor.
Define maximum demand?
how to match 0 -10V with 4 - 20mA
what is meant by 3rd hormonics ?
How much energy save vfd if motor run on 50 Hz (full speed)
If a rotary UPS is in line through grid power; What would be the impact on Power Factor if the load through rotary ups is 25% , 50% , 75% & 100%. Will the power factor reduce with less load?