Why 11KV/440V distribution supply use for Domestic use?
Answers were Sorted based on User's Feedback
Answer / arti
11kV is the transmitted voltage. Voltage is usually
transmitted at higher voltage so as to save the cost of
copper (conductor side).
All the domestic appliances as per Indian standards are
rated at 250V and P-N voltage tapped from a phase of 3-
phase 440V is 250V (440/ sqrt(3)) approx. So 11kV/440V is
used for distribution suply.
| Is This Answer Correct ? | 54 Yes | 5 No |
Answer / sathish
This stage is called as secondary distrbution in this stage they convert ffom 3 wire to 4 wire system. In domestic we need l-n or r-y-b-n
| Is This Answer Correct ? | 9 Yes | 10 No |
Answer / yasuteru
because domestic appliances work on low voltages
| Is This Answer Correct ? | 0 Yes | 6 No |
can we connect PARALLEL 2 D.G set with different rating?? How ? What is the requirement for this connections?
the minimum clearance b/w ceiling and plane of leaf of ceilng fan shall be ..........mm
what is the principle of operation of CFL ??
if we apply 1000ADC instead of 100ADC or We apply 50ADC instead of 100ADC,What will be happened in the test result value.Pl explain
why we are using star connection and delta connection? difference?
you have a 2 tonne ac that operates for 2 hrs daily what will be you monthly bill (this is complete question asked nothing else was given)?
what is meant by vector group of a transformer? How can it be derived?
method to check earthing
I am going to appear for the RRB Chennai Section Engineer online exam. Please send me the question papers from 2001 to date to my mail id: vsujith_rajan@yahoo.co.in
why the emf of a cell more than the terminal voltage when the cell is delivering current?
I have one ct of ratio 3000-2000/1 Amp its knee point voltage mentioned on name plate is 500-333/30mA-50mA at Vk/2. in secondary box there is three terminal named 1S1, 1S2, 1S3 then on which terminal obtained the knee point voltage ie 1S1-1S2 OR 1S1-1S3 & also specify the knee point voltage for the ratio 3000 from name plate.
Why a transformer is rated in kVA and not in kW??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)