Why 11KV/440V distribution supply use for Domestic use?
Answers were Sorted based on User's Feedback
Answer / arti
11kV is the transmitted voltage. Voltage is usually
transmitted at higher voltage so as to save the cost of
copper (conductor side).
All the domestic appliances as per Indian standards are
rated at 250V and P-N voltage tapped from a phase of 3-
phase 440V is 250V (440/ sqrt(3)) approx. So 11kV/440V is
used for distribution suply.
Is This Answer Correct ? | 54 Yes | 5 No |
Answer / sathish
This stage is called as secondary distrbution in this stage they convert ffom 3 wire to 4 wire system. In domestic we need l-n or r-y-b-n
Is This Answer Correct ? | 9 Yes | 10 No |
Answer / yasuteru
because domestic appliances work on low voltages
Is This Answer Correct ? | 0 Yes | 6 No |
Why different Pressure switch used in marine boiler water circulation system
Can I parallel 1 MVA generator with 1kVA Generator? if V, F, Ph Seq and Ph angles are same
how to calculate optimum loading for transformer?
I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel with 4000A Breaker.Already I have 2500A load.Can I connect this load directly to the Busbar since I have PROTECTION IN MY MDP Panel ?
dear friends, we are use 130 hp load run with 0.98 power factor ( 38KVAR capacitor connected ). if we need improve the the power factor to 1 (unity). how much kvar capacitor to be add. have any formula? please share with me.
what is the Knee point Voltage?
WHAT MEANT BY MCC PANEL?
How does a diesel generator works?
Is there chopping current in resistive circuit
what is the maintain in ACB,VCB,MCB,MCCB breakers?
What is Transformer?
Define ohm’s law for a.c (alternating current)?