Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Sir we have 12.5 MVA(110/11KV) transformer (Y-Y)
connected,which tripped showing earth fault,when we charged
transformer it stood OK ,but on connecting 11 KV feeders it
tripped showing earth fault.our service engineers found that
the B phase and R phase phase connecting to neutral broken
from HV OLTC(on load tap changer),and R phase and Neutral is
ok.Dissolved gas analysis shows that accetline content is
high,tan delta value is 12.My dout is it is an internal
fault of transformer,why REF or diffrential relay is not
acted?



Sir we have 12.5 MVA(110/11KV) transformer (Y-Y) connected,which tripped showing earth fault,when ..

Answer / k.prakashchandra

REF relay does not act as the unbalanced current is equal to
NCT current in all respects. And for diff relay, it also
does not act as the corresponding ct currents in HT and
sides for each phase are equal.If there is current in only
one phase ,EFR will trip as current's return path is through
the EFR.But why there is current in the single good phase as
all dist Trs are delta/ star connected ? May be due to star
connected line capacitors or dist trs/loads are also star
connected with neutrals earthed.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

If breaker is undefined position, first step to do.

0 Answers   KSEB, L&T, Siemens,


iam interesting to design the control panel for 3 phase pump motors by controling single phase switches.iam plan to use fuse,contactor & relay for motor protection .how can i select the voltage & amps rating for fuse,contactor & relay plz guide me .if anybody clarify my doubt means it will more helpful for my future .

1 Answers  


why sielent pole is used only in hydro generators and not in turbo generators

1 Answers  


Need help. 3 phase system. Neutral line arced and melted upon connection of connector with 3 phase power. Why would that happen?

4 Answers  


I have 90KW Motor 60 Hz,380V Pf 0,88. after testing the Motor without Load is the no load Current 36 A,but wenn i put load after 2 hours the current increase more than 156 A. Can anybode tell me waht is the Problem?

4 Answers   ABB,


Is HT capacitor rating connected directly to motor terminals , related to motor no load current?

0 Answers  


How many types of AC current?

8 Answers  


Why a transformer Noise during its running condition ?

8 Answers   NTPC,


why dc series motor has high starting torque

2 Answers  


What is a formula to decide the size of the cable of the star delta motor ( From Contactor to the motor 2 runs )

4 Answers  


The Howland current source produces a A Unidirectional floating load current B Bidirectional single-ended load current C Unidirectional single-ended load current D Bidirectional floating load current

0 Answers  


thyristor controlled APFC panel design parameter?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)