Sir we have 12.5 MVA(110/11KV) transformer (Y-Y)
connected,which tripped showing earth fault,when we charged
transformer it stood OK ,but on connecting 11 KV feeders it
tripped showing earth fault.our service engineers found that
the B phase and R phase phase connecting to neutral broken
from HV OLTC(on load tap changer),and R phase and Neutral is
ok.Dissolved gas analysis shows that accetline content is
high,tan delta value is 12.My dout is it is an internal
fault of transformer,why REF or diffrential relay is not
acted?
Answer / k.prakashchandra
REF relay does not act as the unbalanced current is equal to
NCT current in all respects. And for diff relay, it also
does not act as the corresponding ct currents in HT and
sides for each phase are equal.If there is current in only
one phase ,EFR will trip as current's return path is through
the EFR.But why there is current in the single good phase as
all dist Trs are delta/ star connected ? May be due to star
connected line capacitors or dist trs/loads are also star
connected with neutrals earthed.
| Is This Answer Correct ? | 0 Yes | 0 No |
Why LVDT have secondary windings connected in differential 1. Higher out put 2. Based on the out put voltage-/+, helps to identify the direction of displacement 3. To establish a null/ reference point
comparision between ACB and VCB
If 24 KVA AVR having Input voltage 200-400v, Output voltage 415+-1%, what will be the voltage if Load is 13A.
Can I parallel 1 MVA generator with 1kVA Generator? if V, F, Ph Seq and Ph angles are same
explain why tap changer is always connected to high voltage winding side of the transformer.
why should we connect the no load components in a equivalent circuit of transformer in parallel?why cant it be in series.
A 11KV, 1200 A breaker combination fixed in a cubicle for HT motor.Is normally for 11 KV motor fuse is using? if Yes, What range fuse is required?
Can anybody tell the formula to calculate temparature rise in the cable with respect to current?
In response to Mr Bikas. If fault current is 52 kA then what will be the CT specification
For 35 HP motor how much amount of capacitor should be on in kvr to reduce the current bill
i have a motor 55kw how u will calculate cable specification for this motor
How many losses in generators? how we can reduce them? and also in motors,transformers?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)