iam interesting to design the control panel for 3 phase
pump motors by controling single phase switches.iam plan to
use fuse,contactor & relay for motor protection .how can i
select the voltage & amps rating for fuse,contactor & relay
plz guide me .if anybody clarify my doubt means it will
more helpful for my future .
Answer / kuldeep singh
Fuse should be 2.0-2.5 times of full load current,
Contactor shall be 2.o times of fullload cureent ( with
AC23 duty) ,relay should be such that full load current of
motors is in mid the range of relay settings,
Isolater rating shall be 2.5 times of full load current
use 4 Amp fuse for your control circuit and aux contactor
of 2no + 2 nc contact etc
for more ask
kuldeepuee@rediffmail.com
KULDEEP SINGH
B.TECH
IITR
Is This Answer Correct ? | 0 Yes | 1 No |
how to find the ballast lost from the actual wattage? for example i am going to buy decorative type 2x36watts fluorescent light fitting for this lamp how to find the ballast lost? is there any formula?
Cb closed condition if there is a tcs fail whether cb will trip or not
i am in need of AC SYNCHRONUS MOTOR 30KW. ANY ONE KNOWS THE MANUFACTURER OF SAME. ALSO MOSFET AC CONVERTER 20KVA CONT.OUTPUT.
can indirect loading be called as phantom loading?
we can conformed the vector group of the transformer. How?
A heater capacity is 3.0 KW on 415V . if supply voltage is 380Volt . what is heater capacity on 380volt . and how calculate and give formulas . Prakash veer singh Roto power Engg.
what is transformar load balancing ?
Name two low frequency oscillators?
What are books to be referred for KPTCL exam?
The objective of connecting a resistance and capacitance across gate circuit is to protect the SCR against
if two transformers are parallel & both have fault short ckt. impedance of 50KA in each case will it increase or decrease show example?
What do you mean by distribution transformers?