I have 90KW Motor 60 Hz,380V Pf 0,88.
after testing the Motor without Load is the no load Current
36 A,but wenn i put load after 2 hours the current increase
more than 156 A.
Can anybode tell me waht is the Problem?
Answers were Sorted based on User's Feedback
Answer / linu mohan
motor full load current is 155-162A for different categories
of make;so check from which load the motor is connected
ex-compressor,pump or crusher likewise anything
1)compressor- air might have blocked in the filter due to
impurities in the air after few hrs,so motor taking high
current.
2)pump-jamming might have blocked in the filter due to
impurities in the water after few hrs,so motor taking high
current.
if the motor is kept in a closed atmospheric room then due
to heatness after few hrs motor will take full load current
&tripping occurs,so to avoid that; place an exhaust in there.
last option clear that its not a star delta feeder...
if then also problem is not solved&strikes again then it
comes under mechanical head for sure
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / michael
the simpliest answer to your question is in this example.
example you have to lift a 10 kg of rice, you use a little strength in order to lift it, but if your tying to lift a 50 kg of rice, you will exert much effort and strength in order to lift it. it is similar to the motor. if there is higher load the current will increase in order to satisfy the load required..
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / manish parekh
Dear Sir,
The 90KW motor FLC is approx 155Amp so the motor amp
increseing after load so load will be 100% on motor.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ketan patekar
90 KW motor full load current carrying capacity is 236 ampere..
And yes when you connect load than afcourse your motor will carry ampere as per your load.
So here everything is ok.
If your motor carrying above 236 ampere current than there is some fault like your load is high or impeller or frame or design problem etc
Is This Answer Correct ? | 0 Yes | 0 No |
How I can Compare 120v/60Hz versus 220v/50Hz ? Please tell me both advantage and disadvantage ......
In motors how many types of cooling systems were used?
how you can select circuit breaker for 2000kva transformer?
2. Modify your design in question 1.a so that the circuit works according to the following function table X Y F 0 0 Clear 0 1 No Change 1 0 Parallel Loading 1 1 Count 3. Design a circuit that detects the pattern 010 in a serial input X considering: 3.a Overlapping 3.b No overlapping
volts=230 c=10mf a=??
motor work in hat principle generator work in what principle transformer work in what principle pls explain with details or answered to ramadoss.sepc@gmail.com
how can we understand that where we have to use ac or dc coil for solenoid valve and why?what is the different between coil of ac and dc explain please.
What is the difference between lubricating oil and insulating Oil?
IN A DY11 GROUP DISTRIBUTION TRANSFORMER WITH NEUTRAL EARTHED, WHAT WILL HAPPEN TO THE SYSTEM VOLTAGE & THE EQUIPMENTS IF EARTH GETS OPEN ON LOAD?
what are the sections in a high voltage system(eg:incomer,buscoupler,isolator
What is sequence network? Discuss all three types of sequence network.
WHAT IS THE PARTIAL DISCHARGE TEST?