I can follow below trouble shooting steps,
check the error code to see if there was any short ckt or
earth fault, if there was (check for cable termination if
the connections are not burnt out due to short circuit,
check earth resistance and current voltage etc. of the
terminals) eliminate the fault then it should work fine.
Check the control wiring of the breaker check the fuses,
contactor operations etc.
check the under voltage release to see if it did not trip
due to under voltage or over voltage. check shunt trip
mechanism.
check if breaker is not overheated as a breaker may not
close if magneto thermal release is tripped.
check closing coil operation and see whether breaker gets
charged automatically with help of the motor.
if none of the above problem found, Rack out the
breaker(keep it in isolated position)trip the breaker
manually a few times and try closing it again should work fine.
In case it does not happen you can try and by pass the
breaker with help of crocodile pin Jumpers ( In case of
Emergency), but one need to be extremely careful and should
ensure that the incomer supply to breaker is turned off
while doing it, as a high risk is involved. Also you should
be confident that breaker did not trip due to an abnormal
condition.
Note: Some breakers indicate nuisance fault as well
Further,
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ramesh arumugam
Please mention the voltage rating and the type of breaker i.e whether ACB or VCB or vcu
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the difference between electrical choke and electronic choke?
How to Select a Transformer Rating ?
3 Answers Tata Steel Limited, Techno Electric and Engineering, Vedanta,
Can anyone tell me some hints about what type of questions are asked by the interviewer by an Electronics engineer when company is installing an IPP and wants a team of engineers?
What is the practical way to calculate the cable size for known ampere load?
what is meant by neutral compensation factor and where it is used
1hp= how much rpm
How much resistance between neutral earthing and body earthing of Power transformer?
how to syncronize two dg sets
what is brushless alternator?
show the single line diagram of star delta starter with single phase preventer
what is negative d.c. voltage, why this voltage is used in base transciever station.
what is the difference between the following 2 situations ? 1)Line & Neutral=240V Line & Earth=230V Neutral & Earth=10V 2)Line & Neutral=230V Line & Earth=240V Neutral & Earth=10V
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)