How to calculate the cable size in sq. mm. when the load is
given in KW?
Answers were Sorted based on User's Feedback
Answer / ram
FIND OUT FULL LOAD CURRENT OF THE GIVEN EQUIPMENT.
THUMB RULE IS THAT, FOR CU CABLE, IF THE CURRENT IS 6
AMP/SQ.MM THE CABLE STARTS TO HEAT. AND FOR AL CABLE IT IS
2 AMP/SQ MM.
ACCORDINGLY WE CAN SELECT THE CABLE.
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / ych
First we have to calculate FLC and after that must look in
the book.
Is This Answer Correct ? | 3 Yes | 6 No |
For LT motors,
For copper,current carring capacity is 4 times of there
cross section area,
For aluminium,current carring capacity is 3 times of area.
This ratio will continuously decrease as we will go to HT
side motors.
Is This Answer Correct ? | 0 Yes | 8 No |
Why is it that polarization index type test is required for MV and HV motors and not for LV motors?
3 Answers La-Gajjar Machineries, Qatar Airlines,
CFL lamp is what type of load?
what & how to check the lightning arrester
Totally how much power will be consumed in 1 hour cotinuous running of electric train engine?
On Which Pressure PRV is operated.
why C T secondary are rating 5A generaly .
What is the winding resistsnce need to be in a 1000kva, 11kv/415v transformer, between ht winding to lt winding, ht winding to earth, lt winding to earth.?
Suppose an electric motor with a controller is not working. What is the sequence of testing you will do in your troubleshooting?
what is the best way to start a 15 KW motor for pump star-delta or direct on line ? and from how many KW i must use direct on line ?
What is the main difference b/t Earth leakage relay & Earth fault relay.I want protect my LT panel(Distribution Panels)which relay have to propose.......
How to calculate Number of Earthing Pits....???
How does an induction motor start?