calculate multiplication factor of a trivector meter with
line ct ratio 200/5A, line PT ratio 11000/110V and meter CT
ratio 200/1A and meter pt Ratio 11000/110V.
Answers were Sorted based on User's Feedback
Answer / shyam sunder thakur
The meter in this case can carry up to 40A current only as meter CT rating is 200/1,
Multiplication Factor if calculated is under
Adopted(line) CT Ratio X Adopted(line) PT Ratio
M.F =--------------------------------------------------
Meter CT Ratio X Meter PT ratio
200/5X11000/110
=----------------------------= 1/5=0.2
200/1X11000/110
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / k.prakashchandra
If the line CT were of 200/1 ratio, the meter would read
correctly. As the ratio is 200/5, for 200 A primary current
the sec current will be 5 A instead of 1.0 .Hence you have
to divide the reading by 5 ,if it is capable of taking 5A.
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / ajaz kirmani
Multiplication Factor MF = [ (200/1)x(11000/110)]
-------------------------------
[ (200/5)x(11000/110)]
MF = 5
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / jaskanwar
In a CT PT connection if there is a LTCT meter of 200/5 installed instead of HT meter of -/5 A . Then what will be the MF for this situation.
CT PT = 10/5 A
| Is This Answer Correct ? | 0 Yes | 3 No |
What are RMU yard Safety Operating Procedures
how dc ct works?
Can we connect two or more energy meters/Amp meters on one CT set(Three phase).
5 Answers Parle, Watermark Engineering,
How relay works, reverse relay, master relay, os relay, earth fault relay and what is its setting point
why the the phase transformer's nuetral has been grounded
Two CTs 1600/1 and 35/1 are in series. while checking the ratio test of a CT(1600/1),same 1600A will also pass through the CT having ratio 35/1. Will it be harmfull to the ct(35/1),if yes , what will happen.CT secondary is shorted
Draw the DOL starter and star delta starter drawing?
A 60w bulb & a room heater are connected in series.if 60 w bulb is replaced by 100w then what will be the effect on heater out & why?
how to calulate bearing number of any motor ?
pls send previous bhel electrical papers
How to test Power Transfomer vector group in the field?
Is any AC drive(VFD) had a feature of DC injection braking? if available please mention the detail. i.e drive can supply braking torque when the motor in idle state.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)