calculate multiplication factor of a trivector meter with
line ct ratio 200/5A, line PT ratio 11000/110V and meter CT
ratio 200/1A and meter pt Ratio 11000/110V.
Answers were Sorted based on User's Feedback
Answer / shyam sunder thakur
The meter in this case can carry up to 40A current only as meter CT rating is 200/1,
Multiplication Factor if calculated is under
Adopted(line) CT Ratio X Adopted(line) PT Ratio
M.F =--------------------------------------------------
Meter CT Ratio X Meter PT ratio
200/5X11000/110
=----------------------------= 1/5=0.2
200/1X11000/110
Is This Answer Correct ? | 14 Yes | 2 No |
Answer / k.prakashchandra
If the line CT were of 200/1 ratio, the meter would read
correctly. As the ratio is 200/5, for 200 A primary current
the sec current will be 5 A instead of 1.0 .Hence you have
to divide the reading by 5 ,if it is capable of taking 5A.
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / ajaz kirmani
Multiplication Factor MF = [ (200/1)x(11000/110)]
-------------------------------
[ (200/5)x(11000/110)]
MF = 5
Is This Answer Correct ? | 2 Yes | 5 No |
Answer / jaskanwar
In a CT PT connection if there is a LTCT meter of 200/5 installed instead of HT meter of -/5 A . Then what will be the MF for this situation.
CT PT = 10/5 A
Is This Answer Correct ? | 0 Yes | 3 No |
what is the difference between the megger and multimeter operation ?
what is the function of turbo in dg sets
Can i connect all earth pits in ring system..., And wat IS 3043 says...please help me
During the troubleshooting of an inoperative shunt generator, you found the voltage to be 2+ volts; what is known from this. Is it (1). odds are the armature is good (2). odds are there is no field current flowing in field windings (3). odds are the armature is bad (4). both 1 & 2 are correct (5). both 2 & 3 are correct
how to find the transformer neutral copper earthing size
What is the use of conservater, bucchos relay, breather in a transformer?
8 Answers Bosch, Wipro, Zadco,
what is meant by magnetic flow meter ? explain its working principle ?
what is the differance of acb and mcb and mccb
what is the maintain in ACB,VCB,MCB,MCCB breakers?
How is the AVR working?
What is Meter MF if External CT Ratio is 150/1 , PT Ratio is 132/110 Meter CT Ratio is 200/1 & Meter PT Ratio is 110/1
why phase plates are used in transmission line????