calculate multiplication factor of a trivector meter with
line ct ratio 200/5A, line PT ratio 11000/110V and meter CT
ratio 200/1A and meter pt Ratio 11000/110V.
Answers were Sorted based on User's Feedback
Answer / shyam sunder thakur
The meter in this case can carry up to 40A current only as meter CT rating is 200/1,
Multiplication Factor if calculated is under
Adopted(line) CT Ratio X Adopted(line) PT Ratio
M.F =--------------------------------------------------
Meter CT Ratio X Meter PT ratio
200/5X11000/110
=----------------------------= 1/5=0.2
200/1X11000/110
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / k.prakashchandra
If the line CT were of 200/1 ratio, the meter would read
correctly. As the ratio is 200/5, for 200 A primary current
the sec current will be 5 A instead of 1.0 .Hence you have
to divide the reading by 5 ,if it is capable of taking 5A.
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / ajaz kirmani
Multiplication Factor MF = [ (200/1)x(11000/110)]
-------------------------------
[ (200/5)x(11000/110)]
MF = 5
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / jaskanwar
In a CT PT connection if there is a LTCT meter of 200/5 installed instead of HT meter of -/5 A . Then what will be the MF for this situation.
CT PT = 10/5 A
| Is This Answer Correct ? | 0 Yes | 3 No |
i have 2 motor of same rating. on no load condition one motor take 1.6A but other motor is taking 4.8A. what is the reason of this. please explain with proof.
We have given to 3phase supply to ups system & how can coming netural
Is there any thumb rule for cable selection for any current rating ?
What is the requirement of grounding the neutral of single phase generators on load? If the neutral is not grounded, what will be the effect?
can any one help me out by posting something related to rvnl interview for site engineer electrical.? what is the procedure? what kinda question they ask us? how long the interview goes? and any tips? and any thing you want to share?
can i used 400A SFU (for the use of PA fan motor),if my BUSBAR rating is only 315A?????answer me quickly as possible.......thanks
what ll happen to current if two phases get short circuited
what are the names and size of various conductors used in transmission lines
What would be the size of wire used for 2 Ton of window A.C?
in the exciter the power is feeded from battry or control or whatever.and we need it in the generators for the stating . do we need it in the shutdown also?i mean the exciter>
why is the size of earth conductor is half of phase conductor.
1 Answers Century Pulp and Paper, L&T,
Is there any relevant technique to produce power from light and heat energy of the sun simultaneosly from same rays of light?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)