What are RMU yard Safety Operating Procedures
Answers were Sorted based on User's Feedback
Answer / nagarajan
Ring main units not only used for High voltage,for LV
distribution purpose also it is being used.during the
operating of RMU back feedings possibilities are ther so we
must ensure after the isolation because two individual
power sources are connected to the RMU. So first isolate
both the source and make earth main circuit.Discharge if it
is high voltage side.Put lock out and tags caution lables
on the both the sources.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / prabhu gnanasekaran
RMU Stands for RING MAIN UNIT.
iF IT IS Power motor control center there will be 2 i/c
with a tie switch whereas if one fails the bus - coupler
gets closed then the routine loads are supplied this
arrangement is provided inorder to avoid the interruption
in power cut.
RMU also falls on the same concept but there will be 2 or
more incoming cable from different sub station but of same
voltage levels.
RMU comes into picture for uninterpted power supply for
industrial sectors also for other sectors.
RMU IS a big topic on protection and other basic things
which cannot be concluded in this.
it is crisp information that all
| Is This Answer Correct ? | 7 Yes | 1 No |
how to calculate power factor rating according to load? please give the answer in simple language, i'm not electrical side
why to use freewheeling diode ( diode in revers bias mode) across dc coil
Can we use the 60 HZ transformer/rectifier/Motors/Coils in 50 HZ? if not so, why?
If excitation will increase, then what will be the effect on power factor? Will it decrease or increase?
We are installing a 1.6 MVA transformer at our crusher plant and the feeder of HPSEBL is 2 km away at substaion . and a VCB is installed in the substaion which is 2 km away from transformer so we need another VCB near the transformer.
what will happen if delta - star , 400V to 6.6KV step up transformer neutral is not grounded, Neutral is not used but transformer is provided with neutral.
What is the make of breakers, transformers, generators? What are their capacities and ratings?
4 Answers Bharat Bijlee, GHPPL, Tata Motors,
Why TAP changer provided in primary side of HT transformer ? and why not in secondary?
what is the value will come when megger the phase to phase ,phase to neutral ,phasae to ground ?
WHY IS THE POWER FACTOR NOT MORE THAN UNITY.
anti pumping relay function
on whcih cycle does gas turbine works?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)