Answer / nagarajan
Ring main units not only used for High voltage,for LV
distribution purpose also it is being used.during the
operating of RMU back feedings possibilities are ther so we
must ensure after the isolation because two individual
power sources are connected to the RMU. So first isolate
both the source and make earth main circuit.Discharge if it
is high voltage side.Put lock out and tags caution lables
on the both the sources.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / prabhu gnanasekaran
RMU Stands for RING MAIN UNIT.
iF IT IS Power motor control center there will be 2 i/c
with a tie switch whereas if one fails the bus - coupler
gets closed then the routine loads are supplied this
arrangement is provided inorder to avoid the interruption
in power cut.
RMU also falls on the same concept but there will be 2 or
more incoming cable from different sub station but of same
voltage levels.
RMU comes into picture for uninterpted power supply for
industrial sectors also for other sectors.
RMU IS a big topic on protection and other basic things
which cannot be concluded in this.
it is crisp information that all
| Is This Answer Correct ? | 7 Yes | 1 No |
What Different of Ht Side VCB & SF6
During the troubleshooting of an inoperative shunt generator, you found the voltage to be 2+ volts; what is known from this. Is it (1). odds are the armature is good (2). odds are there is no field current flowing in field windings (3). odds are the armature is bad (4). both 1 & 2 are correct (5). both 2 & 3 are correct
What is the recommended voltage gap between Live and Earth and ,Earth and Neutral.If these are exceded what is the solution.
dear all, can any body explain that how to select an induction motor for a specific mechanical load(inertia). is there any formula or calculation then please give me. i shell be very thankful to all of you. Thank,s and Rgard,s.
2.5mva transformer is installed in our company with oltc but it is not working in auto mode ,it is operative in manual mode control wiring is done how can i rectify it?
where lt & ht capacitor used
why inuctive drop is not consider in DC MOTOR
why field winding is placed on rotor winding not on stator winding in case of synchronous machine?
How much sq,mm cable need for 800 amps load
Tell me harmfull effects of over voltage,under voltage,spike,surge,transient & noise.
what are the usual topology of transformers at different substations in the power system and why that particular topology is choosen. what are the limitaions of that topology?
Hydro P.P. run @ 600 rpm,8pole, Nucler P.P @ 1500rpm 4 pole , ThermlP.P @ 3000 rpm 2 pole.Why this diffrence??? when we can generate electricity @ 600 rpm then Why we had incresed speed in NPP & TPP???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)