How to test Power Transfomer vector group in the field?
Answers were Sorted based on User's Feedback
Answer / chicoybolanio
Put the tap position on the nominal taps.
Connect the 4 core cable with MCB on the HV side and the
leads cable at LV side and make sure that
the LV side in open circuit. Then loop together between HV
red phase and LV red phase.
Inject 415V (Switch on the MCB) at HV side and measure the
voltage at LV side for each phase. record results and by
using the test result and following proper scale draw the
vector group of the transformer winding.
Is This Answer Correct ? | 11 Yes | 1 No |
Answer / akr
depending upon vector group we shorted winding provde
voltage & check voltage another terminals terminal decided
by vector group
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / n.l.narasimham
Short R-r,Y-y,B-b and extend 3 phase supply to HV side.
Measure voltages of different combinations viz.R-y,R-b,
Y-r,Y-b and so on... Then plot the obtained results on a
graph sheet duly taking a convenient scale (eg.100v=5cm)
Is This Answer Correct ? | 1 Yes | 2 No |
how do you test the capacitor bank ?
How much amperes needed for starting of 4HP motor?
what is meant by displacement & magnitude ?
The reason why the sending end and receiving end voltage sare almost equal when capacitive load is added.
What is the formula to calculate the no load current of a single & three phase induction motor
In CT,which terminal(s1,s2) need to be grounded?
Suppose an electric motor with a controller is not working. What is the sequence of testing you will do in your troubleshooting?
What is the out put of a CT? How the ratio is decided ?
What will be the average KVA rating of Auto Transformer for 75kw 415V , 3phase induction motor
why the tapping of transformer on ht side??????
12 Answers CTS, OPTCL, Visa Steel,
what is the simple meaning of harmonics?
when is the Ohms law is applicable?