Can we connect two or more energy meters/Amp meters on one
CT set(Three phase).
Answers were Sorted based on User's Feedback
Answer / shariff
More 2 Ammeter/Energy meter can be connected on CT secondary,
provided their burden (VA) rating should be high, otherwise
its accuracy will fall.
| Is This Answer Correct ? | 22 Yes | 2 No |
Answer / abhishek pathak
ya why not. Actually always current is flow in series you put on one wire from ct s1 and connect on first energy meter s1 and put on one wire from s2 of first energy meter connect on s1 of second energy meter and second energy meters s2 connect on ct's s2. Then your current path become OK and there will be same rating in twice energy meter which is actual. like this all phase CT will connect on energy meter. and make paralleled of phase voltage line on meter.
| Is This Answer Correct ? | 18 Yes | 0 No |
Answer / abdul whab
i have an ATS panel in which a single breaker will work all the time but i am installing two different CT's on each circuit breaker. can i use one measuring meter for that as at a time only one source will work.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is Avg. Power Consumption of 2 TR Split A/C???How v can calc. this???
The rotor current is directly proportional to slip. How?
can i know how to design overcurrent setting and earth fault for 11kv & o.433kv system assuming tx 1000kva.
what is dc transformer? how it work?
what is merz price protection
Write the analogous electrical elements in force current analogy for the elements of mechanical translational system.
How Can we calculate the rating of a cable?Show the formula?
Why Hg means mecuiry used in vaccum mesuring unit?
Alternators are invariably star connected why?
No load efficiency of transformer is ___________ than full load efficiency
In case of any eventuality, who is your next of kin?
2 Answers Edison, Foster Wheeler, GE, GE Energy, HP, Infosys, Koch Industries, Roper Industries, Siemens,
If i have 200 test cases and we have to execute but we don't have time to execute all testcases.within 1 hour we have to execute that testcases and prepare the test report.so how i have to resolve this problem? is there is any technique in the testing.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)