Answer / shariff
More 2 Ammeter/Energy meter can be connected on CT secondary,
provided their burden (VA) rating should be high, otherwise
its accuracy will fall.
| Is This Answer Correct ? | 22 Yes | 2 No |
Answer / abhishek pathak
ya why not. Actually always current is flow in series you put on one wire from ct s1 and connect on first energy meter s1 and put on one wire from s2 of first energy meter connect on s1 of second energy meter and second energy meters s2 connect on ct's s2. Then your current path become OK and there will be same rating in twice energy meter which is actual. like this all phase CT will connect on energy meter. and make paralleled of phase voltage line on meter.
| Is This Answer Correct ? | 18 Yes | 0 No |
Answer / abdul whab
i have an ATS panel in which a single breaker will work all the time but i am installing two different CT's on each circuit breaker. can i use one measuring meter for that as at a time only one source will work.
| Is This Answer Correct ? | 0 Yes | 0 No |
what r the checklist while installing 500 kva transformer
IDMT relay are mostly used for protection against..??? 1)Earth Fault 2)Inter turn fault 3)Overloading 4)None of the above
Difference between hopkinson and swinburne's test
I am EEE student i want to improve my core side skills.how cn i approach it?
I just purchased a 4 position cam switch to be used to operate a 3-speed blower motor. The motor is a 10 amp motor and has 3 wires that are used to control speed. The cam switch was rated at 660V 20 amps but when I received it, I noticed that it has AC-15 operational current rating (Ie) of 4/5 amps. If I am reading the label correctly. the 4/5 amps is related to 440v/220V (Ue). Other ratings are AC-3: 5.5A, AC2: 7.5A and AC-4: 1.5A. My questions are 1) Is it safe to use this switch with the motor I have 2) what is the difference between the 20 amp Ith ratting and the Ie operational ratings?
Differenc between the resistance and resisters?
Why we are going for converter transformers for DC drives application instead of distribution transformer?
What is stray current in DC Traction?
DISCUSS THE SHAFT MOUNTED D.C. GENERATOR ,BASED ON EXCITATION SYSTEM IN ELECTRICAL SYSTRM
what is the VA(Voltampire)? define with calculation?
How do you commission a power Transformer?
if we increase the frequency given to a transformer then wat will happen to the transformer size, whether it will increase?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)