what are the main differences of delta and star connection
Answers were Sorted based on User's Feedback
Answer / ittu
In delta their is no neutral point.
In star v can find it.
| Is This Answer Correct ? | 14 Yes | 1 No |
Answer / alen
Delta is when we need much power from motor but in star we
need only the speed.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / sameer
In delta connection line voltage= phase voltage,VL=Vph and
line current=√3phase current, IL=√3Iph.
In start connection Line voltage=√3 Phase voltage ,
VL=√3Vph and line current=Phase current,IL=Iph and in
this connection we got star or neutral point.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / yash sharma
star connection - phase voltage is 1/1.73 times line voltage so speed will be less and required insulation will be low , hence saving of copper achieved. now for delta start you motor which is in your mind!!!!
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / elayaraja
in delta their is speed high but
ster speed slow
| Is This Answer Correct ? | 0 Yes | 15 No |
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
what is the effect of change in supply frequency on load angle of synchronous motor,all other parameters remaining same?
In n high voltage 11kv system What happened if 1 of CT cable (IDMT) loose.Will e/f or o/c trip.please explain detail
IN A SMALL D.C GENERATOR, IF WE REPLACE THE LAMINATED CORE ARMATURE WITH A WOODEN BLOCK OF SAME SIZE & SHAPE AND WIND WIRES WOUND ON THE SLOTS OF WOODEN ARMATURE AND CONNECTED TO THE COMMUTATOR.COMMUTATOR IS FITTED WITH BRUSH TO RECEIVE INDUCED E.M.F.WHETHER E.M.F GENERATED OR NOT?
How to calculate earth fault current for 6.6 KV , 50 HZ , 756 Amps , 3000 RPM , 0.8 PF generator
which one is dangerous AC Power r DC Power for Electrical Shock ?
is earthing is necessary if we use armoured cable
1 Answers ABB, Schwing Stetter, Siemens,
Stator of three phase induction motor creates Rotating Magnetic field.But why not Transformer?
why battery room in substation is black coloured?
I want d.g.set our company
what is the working principle of energy saver control panel. please give the complete calculation & theory.
Refernce currents are to be generated using refernce cueernts how can this be done??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)