if HT side voltage is high current is low . and LT side
voltage is low current is high please explian.
Answers were Sorted based on User's Feedback
Answer / asutosh
for a perticular design the incoming power is same.
we know P = VI so when voltage is high current is low &
viceversa.
| Is This Answer Correct ? | 21 Yes | 0 No |
Answer / jital
Voltage & Current are the inverse propotion ( Voltage is
High, Current is less & Voltage is low, Current is More )
for the Same load when considered on different voltages.
its following P = VI
I.E> For the Same Load in 11 KV Current will be very less
For the same load in 415 V Current will be high compare to
11 Kv
| Is This Answer Correct ? | 17 Yes | 0 No |
Answer / bapi
AS kVA RATING OF A TRAFO IS CONSTANT.
SO FOR HT SIDE MEANS HIGH VOLTAGE SIDE CURRENT IS LESS &
FOR LT SIDE MEANS LOW VOLTAGE SIDE CURRENT IS MORE.
HIGH VOLTAGE X LOW CURRENT = LOW VOLTAGE X HIGH CURRENT
(HT SIDE) (LT SIDE)
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / bhavesh chauhan
Voltage and Current are inversely proportional to each other in Transformers.. As the value of voltage increases current decreases, and as the value of voltage decreases the current value increases.... I Will make you count..
Practically i work in a 220/66/11 kv power station.
I have a 100 MVA Transformer which is a Step Down X'mer. The H.V Side of the X'mer gets 220KV input and L.V of the X'mer gives 66KV output...Now to calculate ............
The Current for H.V Side according to P=VI
we have P=100 MVA
V=220 KV
I=?
I= 100 10^6 /1.732 X 220 X 10^3 = 262.24 Amps
Similarly for L.V
I= 100 10^6 /1.732 X 66 X 10^3 = 874.79 Amps
These are the Actual H.V and L.V Current reading of a working transformer... Which proves that when Voltage decreases current increases..........Thank you
| Is This Answer Correct ? | 6 Yes | 1 No |
what is power and what is watts detailed description and formulas
why colour of electrical equipment( like transformer) is grey
what is purpose of using neutral grounding transformer in generators??
what is the meaning for va and how it is generated
if flow of electrons is current then why their direction are different???
What is meant by Im=30mA@Vk/2. How to know the kee point voltage for CT design
if i have one capacitor=80 micro farad which correct the unity power factor,but i want to make capacitor bank who correct the power factor.so,how to split this capacitance value?
6.6 KV /.415KV Step down trf. we can get 6.6 KV from primary by applying .415 KV secondary side by same TRF.
how balanced in star delta connection ?
During regenerative breaking= A rotating magnetic field is reversed B slip is positive C torque is positive D slip is negative
I have 150/1A Rating CT Suppose if i inject 15A in CT " Secondary" means what will happen ??????
Who we calculate the generator NGR resistant, generator voltage 11 KV ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)