what are the main differences of delta and star connection
Answer Posted / sameer
In delta connection line voltage= phase voltage,VL=Vph and
line current=√3phase current, IL=√3Iph.
In start connection Line voltage=√3 Phase voltage ,
VL=√3Vph and line current=Phase current,IL=Iph and in
this connection we got star or neutral point.
| Is This Answer Correct ? | 2 Yes | 2 No |
Post New Answer View All Answers
What is FM200 Gas??Applications........
PLS MENTION QUESTIONS ASKED IN IOCL INTERVIEW FOR ELECTRICAL EGG??
what can be the causes of capacitor start motor having a higher current that its actual
What are the limitations of Kirchoff's laws?
what is the relation between reactive power and power factor for the what is the limit of reactive power and power factor
Purpose of providing neutral isolation panel for parallel operation of diesel generator
How cmd is calculated in case of energy neters
what is differant beetween overload current and phase current?
What is the direction of current flow in ct secondary...means if the current is flowing from P1 to P2 then what will be the direction of current flow in ct secondaryw
What is the best thing to protect the motor from running over full current. CT or O/L or pressure transducer at the given pressure rating
any one can explain what is the size of pvc,armoured, various sizes of powr cable dia?
A generating system will have a total capacity of 300 MW. Find the probable forced outage when the capacity is supplied by two 150 MW units. The operating probability of all units is P=0.98 and forced outage probability rate Q =0.02 .
What is domestic transformer? Draw the connection of domestic transformer.
What are factors to be considered while we selecting the Core Balance Current Transformer for Earth fault protection
what are the Alarm, Trip & Safety equipment (Issues) present in Power Transformers pls Mail it to ashokbabunhce@gmail.com