how does we do bench calibration of a differential
transmitter.
Answer / himanshu amin
dp trasmitter is having range of few w/c. take example of
you want to calibrate 0-50 in h2o dp transmitter. connect
power supply and multimeter to connection point. connect
small hand pump to high side of dp transmitter. keep low
side of dp open to atmosphere. first check 4ma when both
connection are open to atmosphere. then connect hand pump
to high side and give 12.5, 25.0,37.5 & 50 in h20 and check
8,12,16,&20 ma o/p.
| Is This Answer Correct ? | 8 Yes | 0 No |
Explain working principle of lvdt?
What are continuances of connecting earthing and shield of branch cables (instrument to Junction box), at the same earthing pot provided on JB? Is it ok, or may produce some problem?
0 Answers Process Control Technologies,
how u measure flow?orifice measurement?why all ft in square root?
How to convert ma to mv? Resistance 250 ohm is connected in series or Parallel?
How we can do the linearity test for Bently Naveda Vibration Probe?
how to rectify the problem ,if we erected the DPT instrument wrongly of hp on lp side and lp on hp side?
where can we use viberation transmitter,and how can we control viberation?
what is the square root flow transmitter formulla ?
which type of rtd is good for any system,2wire,3wire or 4 wire
what happen if i increase height of displacer type LT.accuracy or sensitivity are affected.why?
Why we use negetive (-)voltage in vibration system
Pressure transmitter working Principles?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)