how the 4 to 20 mA signal goes to any
controller/indicator,and what is the role of voltage ,12/24
and how to do connection of it, in controller.
Answer / carl_ellis
For a 2 wire loop powered transmitter, a DC power supply
supplies power to the transmitter to power its electronics.
The transmitter uses about 3.5mA of the loop current to run
its electronics.
The transmitter's electronics measures a physical property
(temperature/pressure) which creates a measurement value
associated with engineering units. The transmitter
regulates the loop current between 4.0 and 20.0 mA (by
varying its internal resistance to drop whatever voltage is
needed to create the correct current) so the current
represents a measurement proportional to the scale
configured for that physical property.
The controller/indicator is the primary 'load' with an
analog input that has a dropping resistor. The dropping
resistor creates an IR (voltage) drop the
controller/indicator uses for its A/D conversion.
A 2 wire loop powered transmitter has a lift-off voltage,
the minimum voltage needed to operate the transmitter with a
zero ohm load. As the loop load voltage increases, the
minimum voltage required to power the transmitter and the
loop load increases.
24Vdc is the typical, nominal power supply voltage used in
the process industries. Many 2 wire loop powered
transmitters will function with supply voltages up to about
40Vdc. Higher supply voltages are needed with long copper
wire runs where the wire resistance becomes a significant
load factor.
Carl Ellis
Measure First
| Is This Answer Correct ? | 0 Yes | 0 No |
explain how magnetic flowmeter works
if we mount flow tube in arrow direction then flow comes in negative & if we mount it another direction then flow comes positive,So what will be the problem
Which softwere is required to communicate the S7-300 processor
TEMPERATURE VARIATION FOR FREQUENTLY.
what does a positioner in control valve ?
what is flow
what is the standard of determining opening/closing time of Motor Operated Valve?
we are used SAMSON 3730 Smart positioner.please tell me how to calibration this.
Can i convert 230v ac to 24v dc by using a relay?Instead of Smps is it possible? What is relay logic in plc ?? How it works?
Why capacitive banks ar5e important?
What standards are used for earthing of field instruments?
why can't we use 5-20mA standard or some other instead of 4- 20mA?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)