Question: How to calculate flow of air bubbler type level transmiter? According hight and density?
I love this question because it deals with the understanding of how a bubbler works - flow is not the issue, pressure is.
The calculated value for a bubbler is NOT flow. The critical, calculated value for a bubbler is pressure, because the air/gas pressure in the bubbler tube is a direct representation of the head pressure of the liquid column; which in turn, can be interpreted as the level of the liquid column.
Measurements of head pressure are always done in units of water column (wc), inches of water column or mm of water column, because water column is universal everywhere in the world.
The column of liquid might not be water, it might be some chemical or solution whose specific gravity (density) is not the same as water. So to determine the level, the head pressure measurement of the air/gas pressure in the bubbler dip tube needs to be corrected by the specific gravity. Level = measurement (wc)/specific gravity
The flow rate of air/gas is typically just enough to create a constant stream of bubbles, proving that the air/gas column in the tube has sufficient pressure to overcome the liquid column head pressure. Flow rates regulated by a constant flow, differential relay range from 0.5-2.0 CFH (15 L/hr to 55 L/hr).
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / madani
Suppose level to be measured is 02 meters from the datum line.Fill the vessel with service liquid of 02 meters
height and adjust the purge rotameter flow until Transmitter output reads 20 ma DC.
| Is This Answer Correct ? | 0 Yes | 2 No |
You wish to SINK all my digital inputs to a PLC digital input card. Would you common out the leads to a positive or a negative connection?
How to convert mA into Percentage?
what is the difference between impact plate n coriolis type solid flow meters n how they works....n which one is better
I m appointed as an automation trainee engineer in small firm in that I am only the one , my company give me a project on s7-200 as i m beginner I don't know how to program so please send me the helpful site so that I complete my project before deadline....please help me out in this critical situation.
can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0 to 10 Kg/cm2 ?.. Will it affect 4 to 20 mA output signal which we will feed to the PLC.
what is the minimum power (P=VI)to produce a spark?
the whole paper was based on Transducers..questions like define repeatability, error,accuracy,precision..den there were many q. on the conversion of Pa to mmHg and other units.. also..der wer few Q. on some level sensors(with diagram)
why we use impulse line of flow transmitter at 45 deg. angle both side of orifice plate.
in yokogawa prosef rd safety PLC how to data send frome local SCS to other SCS and other FCS
what is remote mount with MTA option? (In case of Dual Sensor Vortex Flowmeter,rosemount has written in its catalog drawings).
Difine flashing , Cavitaion & Noise? how to minimize these effects
what is RTV function in in process control?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)