Answer Posted / k.prakashchandra
This relay is used to supervise the tripping circuit and to
provide alarm ,independent of breaker status, for 1)loss of
dc supply2)faults in trip coil or cables 3)faults on the
breaker aux contacts 4)faults in the relay itself
| Is This Answer Correct ? | 15 Yes | 5 No |
Post New Answer View All Answers
What is the function of electron gun assembly used in crt?
Is there any specialised book to refer about fault level calculation both in MV and LV side??
How to calculate the volumetric capacity of a oxygen & Nitrogen gas Cylinder if pressure is 145 kg/cm2 & water capacity of cylinder is 67 liters.
when 20hp 3 phase motor start no load condition in star or delta connection.find current and write formula.(tariq)
Can you tell me more about pu systems (per unit systems )calculation in large power systems? how to get the base for voltage and power in generator, transformator and transmission lines?
How many Zones can be in Conventional type fire alarm system & how can we detect the fire in Conv. type FAS?
how to select fuse rating for a 3-phase motor ???
why can we use cosine wave instead of sine in ac supply as both have same rms vale and ripple factor
Why arc quenching is used in Diode ?
why it is not advisable to run low rating (19KVA) DG sets in parallel for long durations even though they are provided with droop ckts (QDC)
What products have you designed which have entered high volume production?
After doubling voltage from solar cells & use step down voltage transformer can we get high current output with low voltage.
wht is embedded systems? what is new inthis field?
HOW TO CALCULATE HV TEST VOLTAGE FOR ELECTRICAL EQPT.
What is pi controller?