A motor works on 30 killo watts.how much ampers will be
required if it works on 440volts?
Answers were Sorted based on User's Feedback
Answer / sanjeev
We have to take motor efficiency also ,i.e
I= kw/1.732*415*cos@*efficiency
Then we will get Exact Amp (Nameplate amp)
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / irfan ahmad
V=440 V
P=30 Kw = 30000 w
we know that ,
P=1.732VI*(power factor)
I=30000/(1.732*440*0.9)
I=43.7 amps [power factor in application is 0.9]
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / gaurang
We Know the Power Equation
P=1.732*V*I*Cosphi
So As per Details
P=30 KW
V=440 Volts
Then,
I=30 KW/1.732*440*0.8
Wher Cos phi=0.8
I=49 A
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / xxx
Calculate Kar le Yar. Power equation to diya hai do bhai
logon ne.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ashok
p=30kw
v=440v
i=?
we know that
p=vi
i=p/v
i=30k/44o
i=68.18
Is This Answer Correct ? | 2 Yes | 4 No |
What is the function of PMG in DG sets & how it works??????????
what is phase to phase voltage? what is line to line voltage
46 Answers Exmar, HBL Power Systems,
we convert 66kv to 33 kv to 11kv to 440v. why can't we directly convert 33kv to 440 ?
in GEAFOL Cast-Resin trnaformer of 11/.72kv which has tapping of 11550v,11250,11000,10246v in primary side. To obtain 700v. which tapping should be used of HV side as we have 11000v/720v tapping now .
how do the stepper motor works.
What are the advantages of speed control using thyristor?
How can we decide the fualt levels of sub-stations?
2 Answers Bhel, Enercon, Prakash Industries,
What is the reason for low voltage in houses?
What meant by XLPE cable
what is the Earth Voltages in Power Plants, Sub-stations, Industries, Residential & Commercial Buildings.
If the output of a 100kva, 415v generator is stepped up to 11kv with a 500kva transformer,can the transformer be Loaded above the source generator loading?
which gas is cost wise high?