A motor works on 30 killo watts.how much ampers will be
required if it works on 440volts?
Answers were Sorted based on User's Feedback
Answer / sanjeev
We have to take motor efficiency also ,i.e
I= kw/1.732*415*cos@*efficiency
Then we will get Exact Amp (Nameplate amp)
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / irfan ahmad
V=440 V
P=30 Kw = 30000 w
we know that ,
P=1.732VI*(power factor)
I=30000/(1.732*440*0.9)
I=43.7 amps [power factor in application is 0.9]
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / gaurang
We Know the Power Equation
P=1.732*V*I*Cosphi
So As per Details
P=30 KW
V=440 Volts
Then,
I=30 KW/1.732*440*0.8
Wher Cos phi=0.8
I=49 A
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / xxx
Calculate Kar le Yar. Power equation to diya hai do bhai
logon ne.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ashok
p=30kw
v=440v
i=?
we know that
p=vi
i=p/v
i=30k/44o
i=68.18
Is This Answer Correct ? | 2 Yes | 4 No |
is oil viscosity affect on motor current?
What are the point of a single core cable to be earthed?
why celing fan is running in anti clock wise and table fan is running in clock wised?
2 Answers Ambuja, Infosys, MAHINDRA,
what is the first step of dg shycroning ?
What will happen if i connect two 3-phase tranformers secondary supply on one bus bar that is R-Y-B-N?
3-PHASE 15KVA dg IS EQUIVALENT TO 12 KW,hOW?
how we can calculate LT side current of transformer
difference between elcb and rccb
how can i change the rotation of the AC single phase induction motor and show me by diagram
how to calculate the loss tangent of electrical cables
We have 800KW motor operating at 6600Volt,50 Hz supply.During 1st startup it tripped on overcurrent trip.It's FLA is 88 Amps.The K factor of Thermal overloaaad was set on .94 initially.then we set at 0.97 and then it started fine.i dont understand why it tripped first?What are the protections which comes in picture during starting ?
What is Delta Connection? What is meant by Forward Delta & Reverse Delta & How Will be the Connection in Power Transformers?