why we use Bus earth truck and Cable earth truck
Answers were Sorted based on User's Feedback
Answer / jaswant rajawat
Bus earthing truck is use to earth bus bars of switchboard
at the time of maintenance of bus bars. For this we have to
remove incomer breaker panel and insert bus earthing truck
so that bus bars will remain earthed during maintenance.
Cable earthing truck is use to earth incoming cable or
outgoing feeder cable in switchboard during maintenance at
transformer end or motor terminal box.
Is This Answer Correct ? | 39 Yes | 3 No |
Answer / sounak chatterjee
In transmission and distribution lines the flow of of power depends upon mode of operation.There are two ways ,one from importing power from grid system,and the other one is exporting power to grid. There are certain switchboards whose sole application is to deliver power from system and as well as importing power from the system. In case of only importing only bus side earthing truck will suffice the purpose but in case of dual operation cable side earthing truck too are required.Since flow of power also from downstream to upstream any recurrence of negative feedback will get diminished by the use of cable side earthing truck.
Is This Answer Correct ? | 1 Yes | 8 No |
Answer / arumugam
Bus earth is also called plate earth. It is using when the
motor KW is higher for example above 20 KW. Incase of any
short circuit in the motor the earth will takes place the
short circuit to earth for protect
Cable earth is using when the Motor KW is below the 20KW.
Is This Answer Correct ? | 0 Yes | 8 No |
Answer / arumugam
Bus earth is also called plate earth. It is using when the
motor KW is higher for example above 20 KW. Incase of any
short circuit in the motor the earth will takes place the
short circuit to earth for protect
Cable earth is using when the Motor KW is below the 20KW.
Is This Answer Correct ? | 0 Yes | 9 No |
What is Diff btw MCP & MCB????
10 Answers Athena, Emerson, Suzlon,
One Township having 850 house and each house load is 2.2KW single phase & 5HP 3 Phase motors of 10 Nos .Who can calculate 11 KV transformer capacity .dilip_bhasker@yahoo.co.in
What happens when reactive power enters a system?
How to calculate per unit impedance of transformer?
what we happen if 400 kvar cpacitor banks are on in manual mode and there is no load on mains ??????????????
What is the Powar consumption of fan low speed to full speed? is it same ?
what are the breakdown voltage rating of mini- curcuit'transfarmer!
what is the power factor
13 Answers Heidelberge Cement,
How is Grounding or Earthing achieved in Planes and Automobiles?
Difference between SHORT CIRCUIT and an OVERLOAD ?
what is difference between line differential and transformer differential?
wat is the function of an inductor? examples.....