1.what to do if ferquency of any power system continue to
decrease ?
Answers were Sorted based on User's Feedback
Answer / sanju
u can bring the frequency to normal by decreasing the laod
shared by the generators. But i dont think any power system
engineer can afford to loose laod. The frequency can be
brought back to the noraml valsue after the following:-
1.make sure that the governor sets of all generators are
working fine.
2.make sure that that the droop characterstics of all the
governors connected are same.
3.make sure that there is no problem with prime mover side.
i hope this wl solve ur problem
sanjeev
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / tarun aggarwal ymca
according to power system engineering the decrease in
frequency is because of load (as load increases speed
decrease) so Automatic control in power system detect this
change in speed and increase the steam or hydro flow to
turbine to counter balance it.
Is This Answer Correct ? | 10 Yes | 3 No |
Answer / nishant
Decrease the load of that system untill the frequency is in
limit
Is This Answer Correct ? | 12 Yes | 6 No |
Answer / sethar12
The problem is not that the frequency of the generator is
decreasing, but the problem is that when this frequency
decreases upto the underfrequency limit of the turbine (or
generator)(frequency bandwidths as given by manufacturer)
(generally at 48Hz). It must be noted that the turbine (or
generator) can run for some commutative duration in
different frequency bandwidths even below 48Hz, but it is
better to avoid in these bandwidths because turbine blades
may damage due to resonance.
The most effective solution is the load-shedding
(distribution side) (by asking the transmission network
controller).
Otherwise reducing the generator load manually.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / balaram mishra
I wii increase the roter speed of the generator, so that
the frequency will increase.
Is This Answer Correct ? | 1 Yes | 3 No |
what is the principle of switch gear? where its function ?
An 11kv system consisting of an underground cable to a sub station about 300 meters away was shut down for about 10 hrs. On energising, it tripped off on earth fault about 10---20 mins later 6 times but since than it is not tripping.its already 3 weeks now. The SPAJ was found to be fine. what could be the cause.No test had been done to determine the cause of the trippings till now because of demand.
what is the reasons for blowing fuse
If the earth is a good conductor of electricity, why don't people get shocked every time they walking on earth?
Pls explan the OLR setting in VCB at HT yard
What is PIR (pre inserting resistance) in 400kv EHV SF6 BREAKER? Why it use?
what are the specifications for Dc cables of higher rating
How much current can a 3-1/2 core 100 mm wire carry?
3 Answers Epitome, Focus, Focus Energy,
How many 2 ton window A/c can runs on a 125 KVA generator?
How we calucate of DC moter I/AMP?
why we use bare wire in high tension power instead of using insulated wire?