Answer / sanju
u can bring the frequency to normal by decreasing the laod
shared by the generators. But i dont think any power system
engineer can afford to loose laod. The frequency can be
brought back to the noraml valsue after the following:-
1.make sure that the governor sets of all generators are
working fine.
2.make sure that that the droop characterstics of all the
governors connected are same.
3.make sure that there is no problem with prime mover side.
i hope this wl solve ur problem
sanjeev
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / tarun aggarwal ymca
according to power system engineering the decrease in
frequency is because of load (as load increases speed
decrease) so Automatic control in power system detect this
change in speed and increase the steam or hydro flow to
turbine to counter balance it.
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / nishant
Decrease the load of that system untill the frequency is in
limit
| Is This Answer Correct ? | 12 Yes | 6 No |
Answer / sethar12
The problem is not that the frequency of the generator is
decreasing, but the problem is that when this frequency
decreases upto the underfrequency limit of the turbine (or
generator)(frequency bandwidths as given by manufacturer)
(generally at 48Hz). It must be noted that the turbine (or
generator) can run for some commutative duration in
different frequency bandwidths even below 48Hz, but it is
better to avoid in these bandwidths because turbine blades
may damage due to resonance.
The most effective solution is the load-shedding
(distribution side) (by asking the transmission network
controller).
Otherwise reducing the generator load manually.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / balaram mishra
I wii increase the roter speed of the generator, so that
the frequency will increase.
| Is This Answer Correct ? | 1 Yes | 3 No |
what is the consuption rating of motor in one day
why table fans rotate clockwise .while ceiling in anti clockwise?
Is it reuired to use house service barcket for 31/2 core 300 Sq.mm cable,if the distance between pole & shop is around 2 mtrs only or can I hang the cable with GI support in air? upto what size of cable GI serrvice btacket is necessary?
Why grables are put in substation?
why knee point voltage should be high in Ct for differential protection
How can we find out LT UG cable fault (size,from-4*25mm sqr to 4*300mm sqr)? How mani types UG cable faults?
how to select the isolation tranformer for siemens 802dsl cnotroller
Why inverter rating in KVA?
Why HRG and LRG used beside transformer, what is the purpose
why we used to transmitt the power at higher voltage why not at lower voltage
why the admittance matrix or y bus matrix of a large network is called sparse matrix?
why we ht line cable size small rather than lt cable.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)