Hello sir
This is prakash from
bangalore i have a doubt why we have to
maintain DG power factor in the range
0.78 to 0.8
Perhaps i f it is increased means what
will happen in DG
Answers were Sorted based on User's Feedback
DG's are usually rated at 0.8 PF lagging. There is no
issues with running the DG at another higher or lower
lagging PF. Usually the output kw of the engine is set at
80% of the kva rating. For example a 100 kva DG will have
an engine rated at 80 kw. This will al;low for a full load
current of about 140 amps at 0.8 PF. Increasing the PF
towards unity the maximum load current must be reduced
until it is about 110 amps otherwise the engine will be
overloaded. If the PF is reduced below 0.8 PF the maximum
current must not exceed 140 amps. This means the kw of the
load must be reduced. This is to stop the windings in the
alternator being burnt.
Going to a leading PF will cause voltage instability and
can cause damage to the alternator.
Is This Answer Correct ? | 1 Yes | 0 No |
Keeping pf at 0.8 lag when running in parallel means the
terminal voltage of gen is higher than the system or busbar
voltage.But it results in higher gen & field currents which
cause unwanted heating of armature and also the field.If
you keep the pf at unity or -ve,the gen does not contribute
to system stability.The generator should also share the
reactive power of the system, which is usually
lagging.Anyway pf may be maintained at 0.9 to 0.95 lag.
Is This Answer Correct ? | 0 Yes | 1 No |
for 12KW motor which cable size has to select for ex.10 meter.
what is the use of spst switch in performing experiment on self excited dc motor?
What are the symptoms of a bad PG card of a drive (inverter) esp. of Yaskawa Ac Drives (inverters) G7 ?
Can anyone explain about Control and power circuits of star delta starter & DOL starter ? How it works? please!
will the introduction of capacitor bank parallel with the induction load reduce power consumption
4 Answers Nokia, WAPDA Water and Power Development Authority,
why skin effect is decreases with decrease with frequency? why skin effect occur
1.How to calculate backup time from series connected battery of 12v dc with 26Ah for 2battery?
What is the d/f b/w MCCB & MCB
Give atleast 20 alternating current apparatus and devices.
What is Difference Between static & Dynamic Pressure of Fan & Blowers
How to choose the vector group for the step up and step down transformers??? Tell me the which vector group is suitable for step up and step down transformers and whats the reason to choose and whats the benefits???
in control panel, how can i measuring the distance between one bus bar to another bus bar. then now only for bus bar. in mpcb and contactor also. that means one mpcb to another mpcb how much distance? how can i calculate that.