Hello sir
This is prakash from
bangalore i have a doubt why we have to
maintain DG power factor in the range
0.78 to 0.8
Perhaps i f it is increased means what
will happen in DG
Answers were Sorted based on User's Feedback
DG's are usually rated at 0.8 PF lagging. There is no
issues with running the DG at another higher or lower
lagging PF. Usually the output kw of the engine is set at
80% of the kva rating. For example a 100 kva DG will have
an engine rated at 80 kw. This will al;low for a full load
current of about 140 amps at 0.8 PF. Increasing the PF
towards unity the maximum load current must be reduced
until it is about 110 amps otherwise the engine will be
overloaded. If the PF is reduced below 0.8 PF the maximum
current must not exceed 140 amps. This means the kw of the
load must be reduced. This is to stop the windings in the
alternator being burnt.
Going to a leading PF will cause voltage instability and
can cause damage to the alternator.
| Is This Answer Correct ? | 1 Yes | 0 No |
Keeping pf at 0.8 lag when running in parallel means the
terminal voltage of gen is higher than the system or busbar
voltage.But it results in higher gen & field currents which
cause unwanted heating of armature and also the field.If
you keep the pf at unity or -ve,the gen does not contribute
to system stability.The generator should also share the
reactive power of the system, which is usually
lagging.Anyway pf may be maintained at 0.9 to 0.95 lag.
| Is This Answer Correct ? | 0 Yes | 1 No |
Hi, I've just got into my electrical engineering course and I need some help with a question of mine here. During a site visit, we were shown a main LT panel which has switchgears, ammeters and different kinds of relays and the distribution network from that panel. In the main LT panel I've noted down the current readings as Ir - 163A, Iy - 150A and Ib - 147A. The Line to Line voltage is 415 V at 50 Hz and Line to Neutral voltage is 230V at 50 Hz. From the above details, how would I calculate the kVA rating of transformer? The primary side voltage of the transformer is 11 kV and the secondary side voltage is 415V and the frequency is 50 Hz.
what should be the minimum rating for using HT Motors?
what is non uniform load
Is it possible we are step down 11 kv to 230v ?
what is ferranti effect?
4.In which type of welding is a pool of molten metal used.....
3 Answers ISRO, SSC, Vizag Steel,
1.differance between onload ups and off line ups.
why we use negative feedback in control system.
explain the existence of reactive power in electrical engg?when it generates?
WHAT IS SITTING AMPS IN OVER-LOAD RELAY FOR 1PH OR 3PH MOTORS?IF ITS NAME PLATE GIVEN MAX AMPS 10AMPS?
what are the standard transmision voltages in india?
we have 350 kva capcitor bank which is not showing KW. dose capacitor shows kW OR not.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)