DG's are usually rated at 0.8 PF lagging. There is no
issues with running the DG at another higher or lower
lagging PF. Usually the output kw of the engine is set at
80% of the kva rating. For example a 100 kva DG will have
an engine rated at 80 kw. This will al;low for a full load
current of about 140 amps at 0.8 PF. Increasing the PF
towards unity the maximum load current must be reduced
until it is about 110 amps otherwise the engine will be
overloaded. If the PF is reduced below 0.8 PF the maximum
current must not exceed 140 amps. This means the kw of the
load must be reduced. This is to stop the windings in the
alternator being burnt.
Going to a leading PF will cause voltage instability and
can cause damage to the alternator.
| Is This Answer Correct ? | 1 Yes | 0 No |
Keeping pf at 0.8 lag when running in parallel means the
terminal voltage of gen is higher than the system or busbar
voltage.But it results in higher gen & field currents which
cause unwanted heating of armature and also the field.If
you keep the pf at unity or -ve,the gen does not contribute
to system stability.The generator should also share the
reactive power of the system, which is usually
lagging.Anyway pf may be maintained at 0.9 to 0.95 lag.
| Is This Answer Correct ? | 0 Yes | 1 No |
how many load we can take for lighting
what is thyristor, how is it works
Our Alternator nameplate specifies a power factor of 0.8. When the Alternator is on light load, the bus bar voltage rises to 11240 volts, whereas the standard value is 10500 volts. Is it ok to increase the power factor to 0.85 or 0.9. I am afraid because the power factor on the name plate is only 0.8 ?
What is making & breaking current ???
Distinguish between shunt and series field coil constructions.
What is EHT tariff or Power factor Tariff ????
Dear all, i completed M.E(Power Electronics & Drives) 2011 passed out having 78% so i need job in core side but i don't know how can i receive the calls from electrical companies and i uploaded my CV in naukri, times jobs etc.. In that iam not recieved any mails from good companies so give me best procedure plzzzzzzzzzzzzzzzzzzzzzzzz..... Thanks, K.Linga Reddy Email-id:-lingareddykmthm@gmail.com Ph no:-08015402078
what happens if we connect two parallel ideal voltage sources across resistor?what is current flowing through resistor?
why the transmission side of the generating transformer is always star??
Now I inject 1kv DC supply r&y=??? R&Y=?? Y&B=?? B&R=???? RYB&N=??? RYBN&E=????? Minimum value====???????
What is the BS(British Standard)code for 11kv motor
what is O.T?specify the acceptable range?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)