Hello sir
This is prakash from
bangalore i have a doubt why we have to
maintain DG power factor in the range
0.78 to 0.8
Perhaps i f it is increased means what
will happen in DG
Answers were Sorted based on User's Feedback
DG's are usually rated at 0.8 PF lagging. There is no
issues with running the DG at another higher or lower
lagging PF. Usually the output kw of the engine is set at
80% of the kva rating. For example a 100 kva DG will have
an engine rated at 80 kw. This will al;low for a full load
current of about 140 amps at 0.8 PF. Increasing the PF
towards unity the maximum load current must be reduced
until it is about 110 amps otherwise the engine will be
overloaded. If the PF is reduced below 0.8 PF the maximum
current must not exceed 140 amps. This means the kw of the
load must be reduced. This is to stop the windings in the
alternator being burnt.
Going to a leading PF will cause voltage instability and
can cause damage to the alternator.
Is This Answer Correct ? | 1 Yes | 0 No |
Keeping pf at 0.8 lag when running in parallel means the
terminal voltage of gen is higher than the system or busbar
voltage.But it results in higher gen & field currents which
cause unwanted heating of armature and also the field.If
you keep the pf at unity or -ve,the gen does not contribute
to system stability.The generator should also share the
reactive power of the system, which is usually
lagging.Anyway pf may be maintained at 0.9 to 0.95 lag.
Is This Answer Correct ? | 0 Yes | 1 No |
Define unilateral circuit?
why are we maintaining some specific gravity in battery ?
what is the AC Plant and how can do the work with parts and picture tell us 150 Tr
What is on line ups and off line ups?
what is power ratio between star & delta connection of 3 phase induction motor
What is the SPEED of electricity?
Is there any difference of regulation of transformer, alternator , transmission line, if yes, what is it?
why the Current transformers secodary is shorted to ground (In metering and Protection)
Why current flows in nutral? As per theory there should be no current in 3 ph explain.
what dose the arrow indicate in the symbol of power transformer?
difference between isolator and circuit breaker?????
our company have 750 kva oil transformer.still we have facing a problem that is when voltage is 11.5 kv coming from HT side then LT-side voltage is 420v or above at tape 1.please give me best solution to decrease the voltage