our company have 750 kva oil transformer.still we have
facing a problem that is when voltage is 11.5 kv coming
from HT side then LT-side voltage is 420v or above at tape
1.please give me best solution to decrease the voltage
Answers were Sorted based on User's Feedback
Answer / sudhakar lanka
my friend, you r looking for reduce the output voltage from 420 volts,
case1: try to keep the primary tap position on maximum voltage
for example ur receiving 11.5kv , if in your transformer there is a tap voltage which is more than these value i.e 11.6kv or else apply 11.5kv on that tap position.
same as above u can try on secondary side also
case2: if u have done all the these exercise, then when u connected to load on transformer there will be voltage drop
check at that time may be ur required voltage i.e rated voltage on motor or machine when it is running on load
other wise u can check with grid supply or substation to get required voltage
Is This Answer Correct ? | 4 Yes | 0 No |
Both the voltages are 5 % higher than the normal voltages ,that means tap position is for normal primary voltage . Check the name plate details
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
From the data furnished by you ,it appears that Tap No.1 is
the normal position as there is 5% rise in both primary and
sec voltages, for 11KV/400V Tr
Is This Answer Correct ? | 0 Yes | 1 No |
IF we have 500kva transformer 11.0/0.415V, 50Hz. How to calculate the current on HT & LT side, how can we consider for its breaker (HT & LT both)? You are requested to solve the question herewith.
3 Answers Bhutan Power Corporation,
why 2 phase is used in argc furnace? why 6 phase is used in converting machinery?
1500Ah VRLA battery,if its weight is designed 125kg during maufacturing its weight is reduced to 85kgs,What will be impact on AH capacity,life & economy?
Phase control and integral control are used for?
1.ZEBRA conductor(large size) 2.KUNDHA conductor( small size ) 3.panther conductor(very small ) 4.lepard conductor (very very small)
How to Decide(calculate) Bush bar size for copper and aluminiam ?
Iwould like to know barc interview questions
why a three phase induction motor cannot run at synchronous speed ?
All the voltage drops and the source voltage added together in a series circuit is equal to
How do determine the Size of a Droop Current Transfomer for Paralleling of Two Generators, Say I need a Droop Current transformer for a 600 kW generator need to be parallel with a 800 kW generator, etc.
2 Answers JK Cement, MPPGCL Madhya Pradesh Power Generating Company Ltd, PNG Power,
what is rating providing of contactor,relay,fuse unit for motor output power
Generator,motor and alternator Working principal Please explain easily