Answer / sudhakar lanka
my friend, you r looking for reduce the output voltage from 420 volts,
case1: try to keep the primary tap position on maximum voltage
for example ur receiving 11.5kv , if in your transformer there is a tap voltage which is more than these value i.e 11.6kv or else apply 11.5kv on that tap position.
same as above u can try on secondary side also
case2: if u have done all the these exercise, then when u connected to load on transformer there will be voltage drop
check at that time may be ur required voltage i.e rated voltage on motor or machine when it is running on load
other wise u can check with grid supply or substation to get required voltage
Is This Answer Correct ? | 4 Yes | 0 No |
Both the voltages are 5 % higher than the normal voltages ,that means tap position is for normal primary voltage . Check the name plate details
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
From the data furnished by you ,it appears that Tap No.1 is
the normal position as there is 5% rise in both primary and
sec voltages, for 11KV/400V Tr
Is This Answer Correct ? | 0 Yes | 1 No |
definition of transponder?
Why you are switching off arc protection mcb when you are taking shutdown for lv board.
is it value of power factor is more than unit. whats effects in the source supply
explain the functions of main isolation switches
How can we increase fuel-power ratio of any DG set?
A 200W,230V lamp is connected across 115V supply.The lamp will draw power?
What is the difference between Isolator & Load Break Switch?
where does 22kv line starts
how we calculate the motor rating of pump for water suction ?its any formula for that plz give thank u
What r the specification furnishid in motor name plate?
What is harmonics in AC waves. How it is generated? How it will effect the system network? how can eliminate it?
Whatis the procedure for getting Electrical (light) licence while Iam a diploma holder in electrical Engg . I Compleated my one yr Apprentice training & worked as a junior engineer (ele) for 2 yr(contract basis).