our company have 750 kva oil transformer.still we have
facing a problem that is when voltage is 11.5 kv coming
from HT side then LT-side voltage is 420v or above at tape
1.please give me best solution to decrease the voltage
Answers were Sorted based on User's Feedback
Answer / sudhakar lanka
my friend, you r looking for reduce the output voltage from 420 volts,
case1: try to keep the primary tap position on maximum voltage
for example ur receiving 11.5kv , if in your transformer there is a tap voltage which is more than these value i.e 11.6kv or else apply 11.5kv on that tap position.
same as above u can try on secondary side also
case2: if u have done all the these exercise, then when u connected to load on transformer there will be voltage drop
check at that time may be ur required voltage i.e rated voltage on motor or machine when it is running on load
other wise u can check with grid supply or substation to get required voltage
| Is This Answer Correct ? | 4 Yes | 0 No |
Both the voltages are 5 % higher than the normal voltages ,that means tap position is for normal primary voltage . Check the name plate details
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
From the data furnished by you ,it appears that Tap No.1 is
the normal position as there is 5% rise in both primary and
sec voltages, for 11KV/400V Tr
| Is This Answer Correct ? | 0 Yes | 1 No |
What is meant by pitch of a synchronous machine.??
State superposition theorem?
If there are two transformer having rating of 2.5mva, 6.6kv/440v(satr-star),and the load is 600kw then what is better to maintain less losses in transformer having both transformer in parellel or only single transformer connected to load? Please give calculated answer
How neutral voltage for transformer decided? eg 33kv neutral voltage for 200MVA transformer?
WHAT IS IEC? & WHAT IS BENEFIT TO PRODUCT FROM IEC?
what is frequency? and its importance
What is the difference between body earthing and neutral earthing?
What are all the problems occured while ac generator running in leading power factor at full load condition?
if the voltage across the lamp drops by 1%, the power drawn will be reduced by how many %?
how to reduce the co level in your 1000kva dg set side?
please send me the L&T Emb. sys. placement papers and entire details of pattren
WHY DOES NEUTRAL DO NOT CARRY EVEN THOUGH IT CARRIES RETURN CURRENT?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)