our company have 750 kva oil transformer.still we have
facing a problem that is when voltage is 11.5 kv coming
from HT side then LT-side voltage is 420v or above at tape
1.please give me best solution to decrease the voltage
Answers were Sorted based on User's Feedback
Answer / sudhakar lanka
my friend, you r looking for reduce the output voltage from 420 volts,
case1: try to keep the primary tap position on maximum voltage
for example ur receiving 11.5kv , if in your transformer there is a tap voltage which is more than these value i.e 11.6kv or else apply 11.5kv on that tap position.
same as above u can try on secondary side also
case2: if u have done all the these exercise, then when u connected to load on transformer there will be voltage drop
check at that time may be ur required voltage i.e rated voltage on motor or machine when it is running on load
other wise u can check with grid supply or substation to get required voltage
| Is This Answer Correct ? | 4 Yes | 0 No |
Both the voltages are 5 % higher than the normal voltages ,that means tap position is for normal primary voltage . Check the name plate details
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
From the data furnished by you ,it appears that Tap No.1 is
the normal position as there is 5% rise in both primary and
sec voltages, for 11KV/400V Tr
| Is This Answer Correct ? | 0 Yes | 1 No |
what is difference between power & distrubution transformer ?
What mean by MLTP
What is the difference between generator and turbo generator - related to power gereration
why we use 50hz frequency in india why not other frequencies like 52,59,42 etc
Difference between ups and invertor
What is reverse power relay?
What is burden of ct,explain very simple
there is an alternator 480 k.w, 400v,50hz, 4-wire running on load having leakage alternator body earthed current 38 A. is it within acceptable limit? if yes then give reference if no then how to bring within specified limit
Explain the Term in CT Name Plate – Class: 5Ps
what are the difference between AC lamp and DC lamp
why we generate transmit and distribute electrical supply in multiple of 11
Hoe to calculate body earthing conductor size ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)