Dear friends, I have a question:
We work on a project which has some boilers to provide steam
for desalination unit.
The boiler area is safe and the only hazard source is the
fuel lines of boilers.
I want to know according to NFPA standard which type of
instrument should be selected on the fuel line: Eex Type or
Non-Eex type?
Thanks in advance
Answers were Sorted based on User's Feedback
Answer / carl_ellis
I totally disagree. Because NFPA 86 (2007) specifically
states that there is no need to impose requirements for
wiring methods appropriate for a hazardous (classified
area).
------- NFPA 86 (2007) ------------
A.4.1.3.3 Unless otherwise required by the local
environment, ovens and furnaces and the surrounding area
are not classified as a hazardous (classified) location.
The primary source of ignition associated with an oven
installation is the oven heating system or equipment or
materials heated. The presence of these ignition sources
precludes the need for imposing requirements for wiring
methods appropriate for a hazardous (classified) location.
Refer to Section 3.3 of NFPA497, Recommended Practice for
the Classification of Flammable Liquids, Gases, or Vapors
and of Hazardous (Classified) Locations for Electrical
Installations in Chemical Process Areas, and Section 3.3
------------ end ---------------
The 'gas train' or 'fuel train' is a pipe carrying fuel.
It is assumed that the fuel stays in the pipe until it gets
to the burner or is bypassed to an equally secure pilot
fuel line.
Control components in the pipeline typically need agency
approvals for conformance to failsafe conditions, but not
for explosion protection.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / swapnil s. dhamanse
First,you should read about NFPA 31 standard.My suggestion
is that you shoud used Eex type instrument on fuel
line,because most of fuel of boiler are flamable,so you
must used flame proof/explosion proof instrument.but,my
question is that why people think too to take decision
about about safety? boiler is highly hazardous area.I know
that outside the fuel line there is less posibilities of
flamable & explosive source but as per NFPA standard you
must use Eex type instruments.
| Is This Answer Correct ? | 2 Yes | 2 No |
why we are giving negative supply for vibration sensors?
Pl send the model question paper of mahagenco account officer post
wht is snap action switch?where it is used?is there any diff between snap action switch and normal pressure switch?
my temperature transmitter in field showing 700 degree , whereas in dcs showing 459 degree, how to resolve this?
WHAT IS INSTRUMENTATION?
How to Calibrate Ultrasonic Level Transmitter in field
how can i calibrate a smart temperature transmitter used by druck 720 process calibrator?
How to calibrate level switch?
how commission a transmitter evev plant is already running
whether radar level transmitter is applicable for the open tank
what is procedure of calibration of remote seal transmiter, botom to top flanch 850mm, fluid liquid density .73, transmiter fixed on a fractionation colum, under vaccume 10mbar
Which of the following instruments consumes maximum power during measurement?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)