Dear friends, I have a question:
We work on a project which has some boilers to provide steam
for desalination unit.
The boiler area is safe and the only hazard source is the
fuel lines of boilers.
I want to know according to NFPA standard which type of
instrument should be selected on the fuel line: Eex Type or
Non-Eex type?
Thanks in advance
Answers were Sorted based on User's Feedback
Answer / carl_ellis
I totally disagree. Because NFPA 86 (2007) specifically
states that there is no need to impose requirements for
wiring methods appropriate for a hazardous (classified
area).
------- NFPA 86 (2007) ------------
A.4.1.3.3 Unless otherwise required by the local
environment, ovens and furnaces and the surrounding area
are not classified as a hazardous (classified) location.
The primary source of ignition associated with an oven
installation is the oven heating system or equipment or
materials heated. The presence of these ignition sources
precludes the need for imposing requirements for wiring
methods appropriate for a hazardous (classified) location.
Refer to Section 3.3 of NFPA497, Recommended Practice for
the Classification of Flammable Liquids, Gases, or Vapors
and of Hazardous (Classified) Locations for Electrical
Installations in Chemical Process Areas, and Section 3.3
------------ end ---------------
The 'gas train' or 'fuel train' is a pipe carrying fuel.
It is assumed that the fuel stays in the pipe until it gets
to the burner or is bypassed to an equally secure pilot
fuel line.
Control components in the pipeline typically need agency
approvals for conformance to failsafe conditions, but not
for explosion protection.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / swapnil s. dhamanse
First,you should read about NFPA 31 standard.My suggestion
is that you shoud used Eex type instrument on fuel
line,because most of fuel of boiler are flamable,so you
must used flame proof/explosion proof instrument.but,my
question is that why people think too to take decision
about about safety? boiler is highly hazardous area.I know
that outside the fuel line there is less posibilities of
flamable & explosive source but as per NFPA standard you
must use Eex type instruments.
| Is This Answer Correct ? | 2 Yes | 2 No |
while i check zero check for dp flow transmitter some fluctuating came (0 to 458 kg/h) what is the reason?
In VVVF DRIVES VOLTAGE IS ALSO VARY WITH THE FREQUENCY. HOW? WHAT IS THE DIRECT FORMULA RELATING THESE TWO.
A differential transmitter is calibrated to measure the flow of lquied, explain what wil happen if the fluid is not pure but contains some bubble?
Introduce yourself which is not present in your biodata?
what is the difference between servo valve & proportional valve
1. How can leveltrol be installed in steam drum for measuring the level of steam drum?
Difference HAZOP and HIRA
how to calculate range of level transmitter?
There are many type of control cable like pair,core,tried, What are defination each one
1 How to calculate dp transmitter steam and water? 2 impulse line for liquid steam and gas
1 Answers Sitara Chemical Industries,
why thermocouple called thermocouple?
what is commisioning procedure,2)what is is the main work in commisioning in the field tx to dcs, plz send me detail
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)