Dear friends, I have a question:
We work on a project which has some boilers to provide steam
for desalination unit.
The boiler area is safe and the only hazard source is the
fuel lines of boilers.
I want to know according to NFPA standard which type of
instrument should be selected on the fuel line: Eex Type or
Non-Eex type?
Thanks in advance
Answers were Sorted based on User's Feedback
Answer / carl_ellis
I totally disagree. Because NFPA 86 (2007) specifically
states that there is no need to impose requirements for
wiring methods appropriate for a hazardous (classified
area).
------- NFPA 86 (2007) ------------
A.4.1.3.3 Unless otherwise required by the local
environment, ovens and furnaces and the surrounding area
are not classified as a hazardous (classified) location.
The primary source of ignition associated with an oven
installation is the oven heating system or equipment or
materials heated. The presence of these ignition sources
precludes the need for imposing requirements for wiring
methods appropriate for a hazardous (classified) location.
Refer to Section 3.3 of NFPA497, Recommended Practice for
the Classification of Flammable Liquids, Gases, or Vapors
and of Hazardous (Classified) Locations for Electrical
Installations in Chemical Process Areas, and Section 3.3
------------ end ---------------
The 'gas train' or 'fuel train' is a pipe carrying fuel.
It is assumed that the fuel stays in the pipe until it gets
to the burner or is bypassed to an equally secure pilot
fuel line.
Control components in the pipeline typically need agency
approvals for conformance to failsafe conditions, but not
for explosion protection.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / swapnil s. dhamanse
First,you should read about NFPA 31 standard.My suggestion
is that you shoud used Eex type instrument on fuel
line,because most of fuel of boiler are flamable,so you
must used flame proof/explosion proof instrument.but,my
question is that why people think too to take decision
about about safety? boiler is highly hazardous area.I know
that outside the fuel line there is less posibilities of
flamable & explosive source but as per NFPA standard you
must use Eex type instruments.
| Is This Answer Correct ? | 2 Yes | 2 No |
if i want buy a pressure gauge then witch parameter i look
Why would an Engineer consider combining FEEDBACK and FEEDFORWARD control in some applications?
hi am durga, i just now completed my eie [2009] , can anyone please guide me what r courses i need to join to enter into core company
Somebody can explain me about >Critical Loops, calibrations, ESD critical Loop checks, Logic Diagram / Cause & Effect checks for ESD loops,
Before erect the instrument what should you do?
what is 24vdc live and dry supply
why is the sleeve of the cable used for?
Guy's need your support,I want to measure closed tank level which is under vacuum -630mmHg using DP Transmitter, tank fluid density 1.38, Tank height is 7ft
What are different types of cable?
what is the use of conrol cable..?
Boiler flame scanner advantage?
0 Answers Fluke, Petrochemicals, Tata Chemicals,
What is procedure on mmwc in to tph
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)