Answer / yomama
Your question suggest you are using a "Differential Pressure
Transmitter" in which case since the -10 Bar vacuum is
applied to both the Hi and Low legs the -10 Bar vacuum is
neutral the Transmitter
In that case we merely multiply the distance (850 mm) x (.73
SG) = 620.5
| Is This Answer Correct ? | 1 Yes | 0 No |
If you installed the remote seal transmitter at flanges,
then in case empty tank /vessel, the transmitter will
showing -mA. so do the followings:
1. Make transmitter 4 mA in this case(without any pressure,
only lower low leg remote seal pressure acting)
2. Apply 850 x 0.73 =620.5 mm of water to high side of
transmitter flange and set transmitter out put 20 mA.
aftabmazari@yahoo.com
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / yomama
Your question suggest you are using a "Differential Pressure
Transmitter" in which case since the -10 Bar vacuum is
applied to both the Hi and Low legs the -10 Bar vacuum is
neutral the Transmitter
In that case we merely multiply the distance (850 mm) x (.73
SG) = 620.5
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ys
close the both hp and lp iso valve(so that any pressure
should not act on tx diaphragm). now measure the input
pressure in mm by connecting hand communicator to tx.. this
is the LRV.now measure span(ie here it is 850mm).multiply
span with liquid density(ie 850*0.73).we will get 620.5.
this is your URV
| Is This Answer Correct ? | 0 Yes | 0 No |
I am working in a process industry, in that there are several sections devided in the SCADA screens and individual sections may START independently. But sometimes i am facing problem i.e, if section 2 Stopped by the operator immediately Section 1 or Section 3 or Section 4 is getting stopped can you expain the reason behind this?
What is mean by trim?
Hot calibrate a level transmitter (wet & dry legs)?
how to measure temperature from resistance of rtd?and how to measure temp from voltage of thermocouple?is there any formulas?
what is the conductivity sensor output formula and what is the ph sensor output formula?
Explain Gas Turbine startup and shutdown sequences
what is the meaning if the control valve CV is 27,in terms of selecting procedure?
what are the steps to follow force a particular input or out put from ics triplex esd system?
1)how can calibrate temperature transmitter? 2)how can calibrate flow transmitter? 3)how can calibrate level transmitter?
3 Answers ccic, Emerson, JK Pharma, NIGC, Rockwell, UltraTech,
i am working in the automation company...i want to just know how actully pid control valves are tune????...
HOW TO CONVERT 0-60KG/CM2 PRESSURE TRANSMITTER TO A LEVEL TRANSMITTER? CAN WE ABLE TO DO IT? IF YES HOW TO DO IT BY USING HART?
How flow can be measured with dp?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)