my temperature transmitter in field showing 700 degree , whereas in dcs showing 459 degree, how to resolve this?
Answers were Sorted based on User's Feedback
1) Most likely, the 4-20mA scaling (what the 4-20mA represents) is not the same on the transmitter as it is on the DCS.
The scaling has to match, that is, be the same on both the transmitter and the DCS analog input.
2) A ground loop will cause an offset. The offset can be negative or positive, depending on the polarity of the ground loop.
Eliminating ground loops can be a major task, so most times, a loop isolator is used to isolate the transmitter from the DCS, which eliminates the ground loop.
Carl Ellis
Measure First
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shahid
Carl Ellis is give the good answer that is the technical error that may occur but some time there is possibility of miss matching in the range of DCS & the field transmitter.That's why should check the both ranges of URV-LRV.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / maheshrp
Reason of DCS and field equipment range different so dcs and field variable reading
So dcs & field range same as problem your solve
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / raghubir nishad
Range Can match in Field instrument or PLC/DCS both side.
| Is This Answer Correct ? | 0 Yes | 0 No |
applications of 1-5v and 4-20ma?
I need control valve ISA hand book. Is there any site to download that big book containing all the pages. Written by Paul Friedmann
Describe the functions of the Operator Interface including the considerations related to alarming and display layout/configuration/layers.
I want to use 1/2 inch SS316 tube in my high pressure & temperature (64 kg/cm2 & 500 deg C)after condensate pot in pressure tranmistter. 1) Is it possible to use 1/2" ss316 tube in high pressure and temperature line. Tube manufacturer is local vendor. 2)On sarting the plant, We need to do system fluse that time condesate is not in the condesate pot so steam is directly contact with the tube. We have no exact calculation to know our tube is ok or nor at this time. pleae,reply.
how to use K thermocouple instead E- type without compesation cable
What is live zero and dead zero
How to calibrate displacer type level transmitter (chemtrol make )for level measurement in hotwell , LP & HP heater ?
How u measure the massflow in orifice flow measurement techniques
what is the difference between venturi and orifice meters?
please tell no. & add. of consultancy who recruit me in power plant as instrumen engg. present i m working in power plant as ass.t instrument engg. thanku mahesh 09226562826
What is the difference between fiber optic cable & Ethernet cable
2 Answers BEMCO, CCC, Pidilite,
what is the difference between auto tuning and manual tuning of controllers(eg:PID,PI,PD CONTROLLERS )
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)