my temperature transmitter in field showing 700 degree , whereas in dcs showing 459 degree, how to resolve this?
Answers were Sorted based on User's Feedback
1) Most likely, the 4-20mA scaling (what the 4-20mA represents) is not the same on the transmitter as it is on the DCS.
The scaling has to match, that is, be the same on both the transmitter and the DCS analog input.
2) A ground loop will cause an offset. The offset can be negative or positive, depending on the polarity of the ground loop.
Eliminating ground loops can be a major task, so most times, a loop isolator is used to isolate the transmitter from the DCS, which eliminates the ground loop.
Carl Ellis
Measure First
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shahid
Carl Ellis is give the good answer that is the technical error that may occur but some time there is possibility of miss matching in the range of DCS & the field transmitter.That's why should check the both ranges of URV-LRV.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / maheshrp
Reason of DCS and field equipment range different so dcs and field variable reading
So dcs & field range same as problem your solve
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / raghubir nishad
Range Can match in Field instrument or PLC/DCS both side.
Is This Answer Correct ? | 0 Yes | 0 No |
1. What means HART communicator / where it is used / how to use it? 2. Types of Thermocouples and its temperature ranges / output of thermocouple? 3. Types of RTDs and its temperature ranges / output of RTD? 4. Idea about Temperature Transmitters? 5. Difference between Analog and Digital signals? 6. Difference between “2 wire” and “4 wire” system / instruments? 7. Difference between “Potential” and “Potential free” contact? 8. Types of flow meters / transmitters? 9. Types of level transmitters? 10. Difference between “Power/Control” cable and “Instrument” cable? 11. What means “shield” and “screen” in cables / how it is useful? 12. Draw a schematic of closed loop circuit of flow / level / pressure / temperature? 13. Idea about calibration of Control valve / positioned / I/P? 14. How to bypass a digital/analog signal in PLC/DCS by hardwire and software?
how to convert MA in to measuring values..and how mwasuring values into MA ?..plz ansr.i have intervw
I faced several time siemens ps2 positioner automatically getting Chang in it's set point direction after auto calibration So is there any causes biside this or any permissives ?
if in a level tx height is given, how u calculate the ranges of the tx?
2 Answers Bombay Rayon Fashions, Invensys,
What is the formula of vabration sesore. i mean how to covert mils to volt plz share if any body knows very argent : my mai is merajalam143545@yahoo.com
How would you choose differential range?
how to caluculate flow by using transmitter?tell me plz I am eagerly waiting for your reply..
2 Answers Agi Glaspac, Reliance Power,
d/p flow transmitter LP side give to pressure.what you geting out put ? how you get(ma)?
Hi all, I am Mohamed from Algeria, I'm a senior Technician qualified in instrumentation. I work in an international petroleum and gas company (SONATRACH: Separation of associated gas from crude oil. Production of condensate, LPG and re-injection of dry gas) within the regulation & Control instrumentation department.I am interested for working in Qatar Petrochemical Company (QAPCO) in Qatar.Now,I am seeking a position, which is an opportunity for me to put my experience to good use and actually participate in running on this company. So, Can anyone help how to contact this company? Thanks Mohamed, mahad8331@gmail.com
What is shriking and swell effect for a boiler ?
what is meant by Valve reversibility?
can any send me a forbes marshall dtron 316 manual