How to calibrate level switch?
Answers were Sorted based on User's Feedback
Suppose you using Float/ displacer type of level switch.
Do the followings:
1. Fill the process into chamber of level switching mark.
2. Contacts of level switch should be changed.
3. If already, closed contacts, then should change to open condition.
4. If contacts not changing, do the knob of switch to change.
Suppose you can not fill process into chamber.(Process may harmful, like ammonia etc).
1. Note the process specific gravity. Suppose it is 0.67.
2. Your height for level switching is 1000 mm.
3. Use water to fill into chamber for calibration instead of process.
4. 1000 x 0.67 = 670 mm
5. So fill into chamber up to 670 mm water. It will operate the switch.
aftabmazari@yahoo.com
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / mahalingam
The switches all are working in Digital mode.Like 0 or 1. To do the calibration confirm the NO & NC. Basically it is NC when the process reaches the desired level then the circuit will be NO.
Is This Answer Correct ? | 0 Yes | 2 No |
If hart communicator provide 4-20ma source to any transmitter during the callibration?
can i use 1 sq mm insted of 1.5 sqmm cable cable length 600 mts under ground laying Cable carrying 24 vdc 4-20ma current
how to install Differential pressure transmitter in gas line.i need transmitter down side.
in the flow caluclation k value how to caluclate.mass flow & volum flow.
What is the logic a Transmitter control a Control Valve? How the signal going to the Control valve? What are systems/Panels/cables/signal used to control valve from Transmitter?
sir ,iam in dem urgent need of HPCL Paper of Instrumentation Branch plz send me at your earliest convenience at ujjwal_sharma1983@yahoo.com
what is stability
What is surge and how is it prevented.
how to calculate the temp. of RTD&Thermocouple when we got some mV r Ohms?if anybody has d chart pls mail the chatrs to me...
if my 6 kva UPS gives 20 min. backup at 100 % load, then at 25% load what is the backup time?
In case of Transmitter's(e.g.Ultrasonic Flow meter ) we have an normal practise of selction of upstream and downstream distance such as (20D and 5D ).can anyone please let me know whow to calculate "D" ?? i guess it refers to pipe thickness is t right ?
what is mean of 3 by 2 automation ?