Suppose you using Float/ displacer type of level switch.
Do the followings:
1. Fill the process into chamber of level switching mark.
2. Contacts of level switch should be changed.
3. If already, closed contacts, then should change to open condition.
4. If contacts not changing, do the knob of switch to change.
Suppose you can not fill process into chamber.(Process may harmful, like ammonia etc).
1. Note the process specific gravity. Suppose it is 0.67.
2. Your height for level switching is 1000 mm.
3. Use water to fill into chamber for calibration instead of process.
4. 1000 x 0.67 = 670 mm
5. So fill into chamber up to 670 mm water. It will operate the switch.
aftabmazari@yahoo.com
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / mahalingam
The switches all are working in Digital mode.Like 0 or 1. To do the calibration confirm the NO & NC. Basically it is NC when the process reaches the desired level then the circuit will be NO.
| Is This Answer Correct ? | 0 Yes | 2 No |
Hi..i am B.E. (elect.&comm.)..i m workini in a bio mass power plant as inst. Engg. I want 2 know about growth in big power plant sector..is this field is good 4 me ..i m electronics engg..? Plz plz reply..
why gray colour is choosing to all instrument panel.why not choosing other colour?
calibration of instruments.
what is the use of conrol cable..?
what5 does intrinsically safe mean.
Is wet leg type system nessesary to measure water level of steam DRUM? How the transmitter is calibrated to measure this level?
what is compensation in engineering and what is temperature compensation?
What is the main difference between Cavitation and Flashing?
how u calibrate pneumatic n motorized c/v?
warning lamp does not light, but it does light when the wire from the lamp going to the sending unit is grounded (the part that plugs into the sending unit) what does this indicate)?
How to convert gpm into inches of eater.I nerd formula with example so pls help me.
A temperature sensor (RTD) connected via a temperature transmitter is adjusted to give an output of 4ma at 60 deg and 20 ma at 600 deg. This output (4-20ma) from the transmitter is connected to an IGBT-inverter to control a high speed (-12,000 to +12,000 RPM) DC motor. And in the inverter it is programmed as, for 4ma the motor speed will be -3,000 RPM and for 20ma the motor speed will be +10,000 RPM. The question is : If the motor speed is +5,500 (RPM), what will be the temperature? (-sign indicates that the motion is in reverse direction).
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)