Can we manually synchronize two DG sets of same ratings
manually without using speed biasing ? If yes then how?
Answers were Sorted based on User's Feedback
Answer / mohammad farman khan-abu dhabi
No, required to be speed biasing
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / deepak thakur
NO, bcoz its very dengerous
For synchronizing two or more DG Set we must requierd
1..DG speed
2..DG voltage
3..DG phase sequence
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
You can use dark or bright lamp method synchronizing .But,
speed control is required.
Is This Answer Correct ? | 0 Yes | 3 No |
Use of electrical theorems (thevenin's,norton's,millmen's,superposition,reciprocity, Maximum Power Transfer theorem,Compensation Theorem) IN REAL LIFE???(IF YOU KNOW EXACT OR CORRECT ANSWER).
2 Answers College School Exams Tests, L&T, PESIT, Wipro,
What should the transformer connection of a 11/220 kV step up and 66/11 kV step down transformer ?
what is a difference b/w earthing & neutral?
After doubling voltage from solar cells & use step down voltage transformer can we get high current output with low voltage.
What is electrical earthing?
1.what is meaning of curve into a mcb. 2.what is basic reason changing of curve
why in a swquence network representation, the negetive sequence generated voltage is taken as zero?
Why cables and busbar both needed in LT Panels?
How to calculat the ratio of HT\LT in energy meter
During he starting up of the motor, the upstream's MCCB (350A) always trips due to the UVT relay activated. Can Star-delta starter use for a 20kW Motor (For a powder mixer machine) cause voltage-dip in the supply line voltage? If so, what are the recommended solution to eliminate/reduce the transient voltage dip in the line voltage?
explain with diagram how to protect transformers and substations from over current with help of CT's?
is it possible to turn on the single phase star delta on delay timer using 24 v dc ?