Can we manually synchronize two DG sets of same ratings
manually without using speed biasing ? If yes then how?
Answers were Sorted based on User's Feedback
Answer / mohammad farman khan-abu dhabi
No, required to be speed biasing
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / deepak thakur
NO, bcoz its very dengerous
For synchronizing two or more DG Set we must requierd
1..DG speed
2..DG voltage
3..DG phase sequence
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
You can use dark or bright lamp method synchronizing .But,
speed control is required.
| Is This Answer Correct ? | 0 Yes | 3 No |
In our factory there is one no. of Series trip HT 6KV OCB. 1. Is it possible to measure CT out put current by 440V Clamp meter? The measurement is required for knowing the exact value of current in CT secondary to set up protection for transformers. 2. plase forward the single line diagram of AMF panel?
Does all the output contacts (N/O as well as N/C) of a Numerical relay operate when relay receives a binary input/inputs or contacts are designated to specific logic input/inputs and only these contacts operate?
by using pump duty, how we will can calculate the motor duty(KW)? is there any standard or formula.
750kva 11/415kv transformer having percentage impedence is5.64%. 11KV HV whose current 39.37A and 415V LV whose current 1043.43A.resistance is 2.5ohm. find no load loss and full load loss?
why Lightning arrestor are made by 2 seperate stack of inslutor but why cvt are in single stack of insulator.
How i can select current transformer and meters for the upgrading the panal..for 200kw to 600kw....i need to select monitoring and protection ct,s and apmpire meter ,kw meter too.
Distinguish between neutral earthing and equipment earthing?
What are the specific gravity of fully charged and fully discharged lead-acid battery?
Why not instal the NGR in 11kv/433kv trasformer?
what is recovery voltage & transient voltage ?
i need to calculate high voltage line power factor daily basics but there is meter reading kwh and kvah while calculating power factor kwh/kvah formula was right. for examble there is point c=13kwh c=1.8 lag c=1.2 lead and c=14.5kvah like that i know that p.f =kwh/kvah but c=1.8lag kvarh and c=1.2lead kvarh points i dont know if u know please reply
Are you connected Transformer neutral eathing with it's body earthing or earthing met of switch yard.? Yes or No ? why ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)