what is recovery voltage & transient voltage ?
Answer / hardik sakariya
when due to any sudden disturbance in the power system any
surge(switching or lightning) is produce than the voltage at
which the Circuit Breaker opens is called the transient
voltage and the voltage at which the circuit breaker extinct
the arc and either isolate or restore the fault is known as
recovery voltage.
| Is This Answer Correct ? | 1 Yes | 0 No |
how to calculate KA rating of C.B?explain with Formula.
What is the criteria for deciding whther fire wall is required between two power transformers
is high voltage or high current is danger
What are the possible causes if load is not same on all the three phases
3-PHASE 15KVA dg IS EQUIVALENT TO 12 KW,hOW?
when we r using 3.5 cable for a bldg. and put laod on each phase using the neutral and neutral is the return paht for the phase so the current of the neutral must be Ir+Ib+iY (return).But the size of the netural is .5 as comper to the phase.
what happens when ac supply is given to D.C motor.
If 110 volts ac is mixed up ith 12 volts dc what will be the resultant voltage and what is the wave form?
why the secondary winding of the transformer is not open circuited ?
5 Answers Nepal Electricity Authority, Torrent Pharma,
How to Calculate the maximum Demand required for a connected load for a manufacturing Plant
how to copy from plc ge fanuc versamax series,all input and output, adress, and printout.
can we use ELCB and RCBO in one db
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)