Are you connected Transformer neutral eathing with it's
body earthing or earthing met of switch yard.? Yes or No ?
why ?
Answers were Sorted based on User's Feedback
Answer / manish
NO, Transformer netural and body earthing connected
saperataly becouse at the time of winding foult and
transformer internal foult foult current transfer with
netural earthing if you are netural earthing joint with met
in that time other electrical equpment can damage.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / prabhat misra
in this case transformer neutral is solidly grounded or it is connected to separate earth pit not with switchyard grid as to overcome any of the fault of switchyard equipmenht and also to protect the switchyarsd equipment from any of the internal fault of Transformer
Is This Answer Correct ? | 0 Yes | 0 No |
Electromagnetic torque developed by the motor is compared to shaft torque. A less B same C depends on motor design D more
what does kirlosker deals with?
Transformer Specification say 66/11KV, 23/27/35MVA OFDAN,what is OFDAN? we know ONAN,ONAF or OFAF
What is the reason behind current flow(20 A) in amain earth cable of an SMDB? Is cuurent flow(45A etc) through a neutral cable acceptable?
explain which quantities change in the starting and the and the running condition in induction motor
When in a large power system if the demand of power is larger than the generated power the frequency of the power system drops.(assume the rated frequency is 50Hz and now it is 49Hz) So does this mean the demand is totally supplied with a lower value of generated power in a lower frequency?
formula for calculation of switchgears(i.e. contactor, fuse, cb, relay etc.), if load current is given?
Why generating voltage is limited up to 22kV?
Efficient electrical earthing in hard rock area
If a rotary UPS is in line through grid power; What would be the impact on Power Factor if the load through rotary ups is 25% , 50% , 75% & 100%. Will the power factor reduce with less load?
what is the prosses for getting of 33kv licence (i have completed my engineering degree & working in 33kv substation for contract basis )????
We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Make Atlas Copco 5.5 kva) that time we face the lot of fluctuation on Dg output. Can you please suggest me how can prevent this fluctuation?