Are you connected Transformer neutral eathing with it's
body earthing or earthing met of switch yard.? Yes or No ?
why ?
Answers were Sorted based on User's Feedback
Answer / manish
NO, Transformer netural and body earthing connected
saperataly becouse at the time of winding foult and
transformer internal foult foult current transfer with
netural earthing if you are netural earthing joint with met
in that time other electrical equpment can damage.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / prabhat misra
in this case transformer neutral is solidly grounded or it is connected to separate earth pit not with switchyard grid as to overcome any of the fault of switchyard equipmenht and also to protect the switchyarsd equipment from any of the internal fault of Transformer
Is This Answer Correct ? | 0 Yes | 0 No |
What is the difference between Neutral And Earth ?
howmuch current can carry the 2.5Sqmm copper cable?
in thermal power plants by opening the turbine governor valve increase the generator load. how
i have a 4 Mva transformer 34.5 kv / 480-277 v and i used 2 parallel 3200 amp bus duct for the secondary feeder using 3 ply of bus bar ( 3/8" x 5" ) as a common where the flexible link terminated and 6300 amps breaker for the main, the lower bus duct reaches 70 degrees and the upper bus duct reaches 55 degrees when i used thermal scanner. why the temperature is not balance when the load reaches 3600 amps.
1. which type of transformer connection is preferred in case of power supply transformers? (A) Star/Star (B) Delta/Delta (C) Star/Delta (D) Zig Zag/Star 2. In a power transformer usuall which winding is closer to the core? (A) Primary winding (B) Secondary winding (C) Low Voltage winding (D) High Voltage winding 3. The power factor of a purely inductive load is (A) Zero (B) Lagging (C) Leading (D) Unity.
9 Answers CECRI_Central_Electrical_Research_Institute,
Can transformer develop three phase power from a single phase source?
what is a 3 phase power formula ?
Why in DC drive u r using in Klin operation in Cement Plant?
what is the rating of boiler?
Z transform is use when system is not a) converges b) diverges
In a 11kv/433v transformer,at the LT side ie 433 V side why do we need to put 3.5 core Cable upto Panel.The full load rated Amps is 666 at LV side.What value of current will flow through the Nuetral Conductor.Why can't we use 4Core Cable instea of that?
what is the saturation point of crgo lamination.