750kva 11/415kv transformer having percentage impedence is5.64%. 11KV HV whose current 39.37A and 415V LV whose current 1043.43A.resistance is 2.5ohm. find no load loss and full load loss?
Answers were Sorted based on User's Feedback
LV side ( DC )resistance can not be 2.5 ohm for a current of 1043.43A. Taking usual losses at 0.08 % + 0.08 % , no load loss is 0.6 KW and that at full load 1.2 KW
| Is This Answer Correct ? | 0 Yes | 0 No |
Dear all i want to know FEWA Electrical Supervisor Licence test Previous Year Questions ? If any body know please send to me shibin_75@yahoo.com
The D.C. spark test is applicable to single conductor cable & assemblies of insulated single conductor cables without insulation shield,metallic sheath or metalic armor?
How will u calculate wire size according to current rating?
what ll happen to current if two phases get short circuited
What is spill current in protection relays?
What is the technical reason for adopting color coding of three phase system as RYB.
How instantanious short circuit current is calculated? its formula?
which type of questions asking for solar companies?
what is acceptable leakage current for 33kv cable while doing high voltage test for cable? how to calaulate the leakage current for 33kv or any rated cable?
What happens if the Capacitive Voltage Transformer Primary neutral is not earthed. There is a CVT between Transformer and source, and the CVT neutral of the transformer is not earthed, does it effect the transformer while charging or does it effect the transformer charging process.
If i switch on a transformer but with no load connected to the secondary path.Is the transformer will burn?
I do wonder why current is present in neutral wire?i check single phase lead current feeding air conditioner...on its phase its current was 10A while same was 10A in neutral...as we know in neutral voltage is zero so if voltage is zero then how current appears on amp meter? my second observation is (just imagination)when I touch phase wire it give me shock but when i touch neutral nothing happens although as above its carrying current(amps) third but with same logic...as in simple Alternate current sine curve there is + and there is negative peak.means every time phase changing so how come every time same phase and same neutral stand (pardon for english mistakes)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)