WHY ARE THE LT GENERATORS SOLIDLY EARTHED WHILE THE HT
GENERATORS ARE EARTHE THROUGH NGR OR NGT??
Answers were Sorted based on User's Feedback
Answer / sanjay kolambekar
Small Generator's are usually a low voltage or
highimpedance in case of HV generator with lower rating
hence the fault current will be less and equipments can
withstand the same. Where as in case of HV Generators with
larger ratings the voltage level is high or the impedance
is low hence the fault current is much higheer. In order to
limit the Fault current to the required level suitable
rating of resistance needs to be introduced between the
Generator neutral and Earth.
| Is This Answer Correct ? | 10 Yes | 0 No |
in HV Generators with larger ratings the voltage level is
high or the impedance is low hence the fault current is
much higheer. In order to limit the Fault current to the
required level suitable rating of resistance needs to be
introduced between the Generator neutral and Earth and to
protect the insulation of the generator and getting heated
up while fault uccurs
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.prakashchandra
Electrical energy is directly is utilised in case of small
alternators whereas it is not so in HT generators.
| Is This Answer Correct ? | 0 Yes | 5 No |
If Earthing is poor in a DB of of Residential Building, will residents feel a leakage voltage in a Electrical Ssytem? is this statement true?
1 Answers Dolphin International,
What is the rating of a circuit breaker needed for 300 kv load in 33KV supply line of 33/415 transformer ? Whether 800/1200 amp vaccum circuit breaker can perform for a 33 KV line in input in 415 volt in output of the transformer ?
What is the use device of the grid.
If load is 240 kw & pf is 0.8 lagging, than how to increase it from0.8 to 1.0(unit),which rating capacitor used, please give me Calculation. What is effact of consumer & suplier if pf is lagging or leading with on effect machines/ TF/GE etc.
Is LV shorted in magnettic balance test?If yes why?
Which modulation has higher data rates a.fm b.am c.qam d.qpsk
Megar test tell sufficient resistant
what is phantom load, Give any example
first 3 men were there .again 3 came.total how much?
what is main reason for grid earthing for any industry
how to decide the load on secondary of the tranformer
xplain in detail d pr. of synchronous motors? why syn. generators r used for the production of electricity?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)