WHY ARE THE LT GENERATORS SOLIDLY EARTHED WHILE THE HT
GENERATORS ARE EARTHE THROUGH NGR OR NGT??
Answers were Sorted based on User's Feedback
Answer / sanjay kolambekar
Small Generator's are usually a low voltage or
highimpedance in case of HV generator with lower rating
hence the fault current will be less and equipments can
withstand the same. Where as in case of HV Generators with
larger ratings the voltage level is high or the impedance
is low hence the fault current is much higheer. In order to
limit the Fault current to the required level suitable
rating of resistance needs to be introduced between the
Generator neutral and Earth.
Is This Answer Correct ? | 10 Yes | 0 No |
in HV Generators with larger ratings the voltage level is
high or the impedance is low hence the fault current is
much higheer. In order to limit the Fault current to the
required level suitable rating of resistance needs to be
introduced between the Generator neutral and Earth and to
protect the insulation of the generator and getting heated
up while fault uccurs
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.prakashchandra
Electrical energy is directly is utilised in case of small
alternators whereas it is not so in HT generators.
Is This Answer Correct ? | 0 Yes | 5 No |
how to calculate capacitor bank value to maintain unity power factor plz xplain with some suitable xample?
what is the mho relay
What is Surge arrest? How it work?
What is an alternator impedance value?
Which motor has more efficiency ;Synchoronous or Induction motor ?
What is meant by Guard relay ?
why we are using auto transformer in sub station mostly???
IF ANY MATERIAL AVAILABLE IN MARKET FOR MOTOR PROTECTION INSTEAD OF OLR & CONTACTOR ?
What happen in ups if phase reverse?
why occ characteristics of generator is also called as magnatization characteristics ?
How it can worked plc based electrical system And which type of software using.