A resistor,inductor and capacitor are connected in series
respectively.Voltage across resistor is 40v,across inductor is
70v,across capacitor is 100v.Then what is the total voltage
applied across the elements?
Answers were Sorted based on User's Feedback
Answer / sai phani kumar
Voltage across resistor Vr= 40
Voltage across inductor Vl= J70 (Since current lags volage
by 90 degress)
Voltage across capacitor Vc= -J100 (since current leads
voltage by 90 degress)
Total voltage = Vector sum of Vr + Vl + Vc
= 40 + J70 -j100
= 40 - j30
Magnitude of voltage = 50
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / t e rao
sai phani kumar answer is correct.
Current flow will be same in all the elements. so
calculation should be done with reference to current.
Voltage across resistor Vr= 40+j0
Voltage across inductor Vl= 0+J70 (Since volage leads the
current by 90 degress)
Voltage across capacitor Vc= 0-J100 (since voltage lags the
current by 90 degress)
Total voltage = Vector sum of Vr + Vl + Vc
= 40+j0 + 0+J70 + 0-J100
= 40 - j30
Magnitude of voltage = 40-j30 = 50Voltage (with 38.6deg lag
to the current)
Is This Answer Correct ? | 6 Yes | 1 No |
What are the advantages and disadvantages of the dc motors?
What is the concept of voltage & current its relation?
Why the voltage n frequency of the incoming generator is kept slightly higher than d grid voltage n frequency while synchronization ?
Hi, My question is our total motor load is 55 kw.so what cable size required for main supply. Please reply
why we have to particulary use ACB for below ratings,even available of MCB,MCCB with that range ?
2 Answers QRG Health City, Siemens,
what could be the possible reasons for copper cable to have low insualation?
WHAT IS THE ROLE OF ELECTRICAL & ELECTRONICS ENGINEER IN TCS.
When calculation of fault current and fault Kva is to be done,why always we use per unit value and why we consider the base kva?
Define maximum demand?
How do you reset circuit breaker?
1 Answers Bhel, Kaveri Steels,
how can we change the supply frequency?
will the turbogenerator operate on leading power factor with out modification in the stator winding.