Please explain about FAT? What is the difference between
FAT and SAT?
Answers were Sorted based on User's Feedback
Answer / manoj
FAT = Factory acceptation test
SAT = Site acceptation test
when any company going to install new instrument control
system,they have to test how its working ? In the FAT shop
they will do configuration setting for all instrumet loops.
according to configuration the system providor will do
function test by simulating signals.
but during the SAT they will check all function with real
Input signals.
Is This Answer Correct ? | 37 Yes | 2 No |
Answer / ajay
FAT: it is the acronym of Factory acceptance test i.e.
Tests performed under simulated conditions at
manufacturer's place witnessed by approving authority
client/End user.
FAT is performed to check the correctness of the system
being supplied. FAT covers all checks over hardware,
interfaces, logics & control loops and system configuration
as per the procedure defined in FAT document.
FAT is performed for Control/DCS & PLC panels.
SAT: it is the acronym of Site acceptance test i.e. tests
performed under live signals received from instruments
installed in plant during the actual commissioning of the
system at site/ end user's place. During SAT, all live
signals are checked and individual control loops & logics
are performed accordingly.
Once all individual loops and logics are checked, then only
plants process is left to run through control system itself.
Is This Answer Correct ? | 20 Yes | 1 No |
FAT: It will be conducted at System Supplier's place with
presence of EPC and End user.They will check the
functionality of Control loops and logics with use of
Simulators.Third part devices will also physically
connected to the system supplier and functionality will be
checked and corrected.
SAT: It will be conducted at End user's place.Here field to
system will be checked and corrected.
Is This Answer Correct ? | 13 Yes | 0 No |
Answer / visakh
hello shanker
these to tests are nothing but to check all the instruments
or materials are in good condition(means damaged or not)
Is This Answer Correct ? | 1 Yes | 11 No |
List three types Level Gauges with their working principles
In Boiler Drum Level- Level control valve how can it tuning (PID)?
Name and describe at least 4 status indicators, typically found on a PLC
Technician A says the brake warning light is connected into both the parking and service brake systems. Technician B says the brake warning light will come ON only if the service brake system fails. Who is correct?
With N nodes and B branches what will have a network ???
In Increasing temperature why thermocouple used and RTD is not used. Both RTD and Thermocouple have in Range of uses.
i have a dp tx range is 5000mmwc. in which calibration i use in a open tank.1.5*3.5*2.5 mtr.for level msmnt. what is the calculation.
give classification of transducer based on type of application
what is dry leg and what is wet leg?
what is commissioning.
How to check vortex flow meter is in good condition while we do not having calibration setup?
Is an analogue only transmitter as accurate as a smart transmitter?