if field commnictor 475 does not communicate with transmitter
what will you do ?
Answers were Sorted based on User's Feedback
Answer / mallu byali
We have to conform before connecting the hart communicator
into tx whether it is smart family or not if may other then
connect the resistance series into the its terminal do the
calibrate.
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / carl_ellis
1) Check for 24Vdc? Yes, but assuming the power supply is
24Vdc, don't expect the voltmeter to read 24v, unless you're
back in the control panel where the power supply is.
If you're out in the field where the transmitter is, you are
not close to the (-) side of the power supply, so where do
you put the black voltmeter probe? The only place for it
on the transmitter's (-) terminal, but measuring voltage
across the transmitter's (+) and (-) terminals only shows
what the transmitter's voltage drop is, not what the source
voltage is.
There is the voltage drop across all parts of the loop, the
transmitter, the load and the wiring. So checking voltage
across the transmitter's (+) and (-) terminals will never
show a full 24Vdc because of the voltage drops in the loop.
With short wiring runs and a 250 ohm load resistor, the
voltage across the (+) and (-) transmitter terminals might
be as high as 23V @ 4.0mA output, but could be as low as 10V
with a 20mA output across 500 ohms.
2) Checking to confirm that the transmitter is a smart
transmitter is a good idea. There are protocols other than
HART or Foundation Fieldbus (Honeywell's DE), and there are
lots of 'dumb' transmitters, too.
Some brands, like Siemens, allow HART to be enabled or
disabled, so the transmitter may be HART capable but have
the HART comm disabled.
3) Connecting a resistor in series is a good idea if the
load resistor is an unknown.
The article at the link below tells why a HART loop needs at
least 230 ohms of resistance
http://blog.lesman.com/2011/10/06/add250-ohm-resistors-to-make-hart-work/#more-68
The temporary use of a 250 ohm resistor is typical because
they're so common in a process plant.
4) Is the HART device at address 0 (zero)? The
communicator can talk to any address, but when connecting
point-to-point on home run wired transmitters, the
expectation is that the transmitter will be at HART address 0.
5) Experience will show that there are the inevitable
problems like
- broken or corroded communicator leads or clips that can go
'open' or be intermittent.
- power supply ripple or EMF induced noise on the loop
circuit can conflict with HART's 1200 baud FSk digital
communications
- some loop device, like a loop isolator or HART-unfriendly
loop indicator has stripped off the HART signal with a low
pass filter, leaving only the 4-20mA current signal
- wrong version DD so the communicator will connect but only
perform the so-called "common commands".
Tell 'em Carl sent you.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / abu maryam
In my opinion there are several causes of this problem:
1- Check the power source if it 24 volt or not.
You should disassemble the power source if it is 24 on out side and still 24 after connecting to device this mean that the power source is good but if it is 24 volt out side and zero after connecting this mean there is found problem in power source (may be problem in module).
2-Read device data if it support hart protocol or not.
3-Disassembled device and connect separate power source and connect 250 ohm series if it no benefit added change the resistance from 250 to 1000 ohm and try or disassemble the resistance and power source and apply power source from multi function calibrator which has internal resistance then try to connect.
4-May be device support hart but hart property is disabled by definite internal jumper in device so we should change this jumper according to device manual.
5-May the device support hart its data files is not added to hart communicator for 1 of the following 2 reasons:
the first:hart communicator is not updated.
The second:the device data filed is not added to hart communicator and it need its special programs and its special cable as found in foxporo transmitters.
6-May the connectors or cables has problem so use another cable.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / marut_tripathi
first check 24 vdc power have or not in transmitter.
termination proper or not of transmitter.
Is This Answer Correct ? | 1 Yes | 2 No |
What is controller? What is transmitter?
Name four general (not technical) criteria that would you consider important, when deciding upon a particular control valve?
Sir, my yokugava FF TYPE LEVEL transmitter us bad, i don't have spares available, i want to replace it with a Rosemount FF transmitter, please tell me what procedure to be followed and what changes to be done in dcs part.
1 Answers BPCL Bharat Petroleum, OEG,
Define the terms Accuracy, precission, Spam, process tolerance while doing calibration of an instrument? Explaini with an example?
why fuse block is not used for AI signal?
What is differnece between leveltroll and interface leveltrol?
Good evening all I need a small favour regarding reliance paper i wanna probable sample papers(e&i) of reliance. if any of u have any idea about dis then plz mail me back.i belongs to electronics and instrumentation engg.so i need e&i papers. thanking u....
can someone tell me about electronic speed switch &how it conect with proximittyswitch?(with dgm)
what is buoyancy law?
WHAT PRINCIPLE OF GAS ANALYSER( CO,CO2,N2)
why t/c is connected parallel and what is the purpose of it
Explain the use of hair spring in the pressure gauge.