Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How CT & PT ratings are decided for a 11KV or 33KV
transmission line?

Answers were Sorted based on User's Feedback



How CT & PT ratings are decided for a 11KV or 33KV transmission line?..

Answer / balasubramanian

CT PT ratings are decided on
1. Class : Protection, metering (for CT)
2. Burden: The load of relays, cabling, etc.
3. Fault level: The thermal capacity of CT for bearing the
fault current for required time 1 sec, 3 sec etc.
4. The voltage level of the system

Is This Answer Correct ?    19 Yes 1 No

How CT & PT ratings are decided for a 11KV or 33KV transmission line?..

Answer / pradeep kumar

ct decied as per metering OR protection ct Use ct as per
metering that we can use the metering instrument of panel
OR control room 1A OR 5A

Is This Answer Correct ?    13 Yes 4 No

How CT & PT ratings are decided for a 11KV or 33KV transmission line?..

Answer / d.durga prasad

In CT

CT primary rating will be decided by its load current &
secondary will depend up on purpose of of selection (either
metering or protection )

In PT

It will always depend upon its system rating & in secondary
the class will be depend upon its purpose of its
utilization as same as in the CT secodary. but the voltage
level is always 110V in secondary of transformer.

Is This Answer Correct ?    5 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

what is different between DIGITAL and ANALOG?

2 Answers  


my question is Megger of cable insulation or swgr board meggerring some values in one day 50mohms,some other day checking different values(20Mohms). this tell that some person tell that that values ok. how to identify the megger value is correct. pls tell me the answer.

2 Answers  


We have a 12MW power plant & we inject 5-6MW power to Orissa GRID. For this we have a 33KV/11KV switch yard having 12.5MVA power transformer. Some times we draw power during emergency. It is observed that during Export or Import for load less than 500Kw the power factor is decreasing to 0.3 . This is happening only during export or import. During island condition TG power factor OK.Our capacitor bank is provided with our Power plant auxilliary load. Please suggest how I can we improve our power factor during low load (GRID).

3 Answers  


explain the meaning of harmonic resonance

0 Answers  


Should transformer earthing pit, to be connect to earthing mat in Substation

4 Answers  


What is the principle of residual protection?

0 Answers  


What would cause a 240v choke that should give 110v out on a 16w lamp to gradually increase to 160v?

0 Answers  


CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415

0 Answers   DEWA, Growth,


How will A Medium voltage circuit breaker(11 kV voltage level) operate under short circuit fault condition whether It is having short circuit release like Low voltage circuit breaker or relay should be given?

0 Answers  


what do you mean by earth fault in transformer?

2 Answers   L&T, UPL,


How to design inductive load for 3 phase 440v and maximum 5 amps for star or delta? Can we use a 15kW, 1450rpm motor for 15kW, 960rpm apllication?If yes.how......n.if thesame motor used what`s it`s sideeefect.

0 Answers  


Dear sir, I am working in wind mill division , pls explain Pls explain in details with formula My question is Wind speed 3.5 M/s Gen RPM is 1500 ( 25 K/w Production ) Wind speed 12 M/s Gen RPM is 1500 ( 220 K/w Production ) Why in 3.5 m/s generation was low , why in 12 m/s generation was high , Pls dont explain wind force or wind density , that one already i know For the above question RPM was same why the KW was different Answer : 1. Its depends on the density ( Force ) of the air Sir , Pls explain wit Formula sir

1 Answers   Vestas,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)