How CT & PT ratings are decided for a 11KV or 33KV
transmission line?
Answers were Sorted based on User's Feedback
Answer / balasubramanian
CT PT ratings are decided on
1. Class : Protection, metering (for CT)
2. Burden: The load of relays, cabling, etc.
3. Fault level: The thermal capacity of CT for bearing the
fault current for required time 1 sec, 3 sec etc.
4. The voltage level of the system
| Is This Answer Correct ? | 19 Yes | 1 No |
Answer / pradeep kumar
ct decied as per metering OR protection ct Use ct as per
metering that we can use the metering instrument of panel
OR control room 1A OR 5A
| Is This Answer Correct ? | 13 Yes | 4 No |
Answer / d.durga prasad
In CT
CT primary rating will be decided by its load current &
secondary will depend up on purpose of of selection (either
metering or protection )
In PT
It will always depend upon its system rating & in secondary
the class will be depend upon its purpose of its
utilization as same as in the CT secodary. but the voltage
level is always 110V in secondary of transformer.
| Is This Answer Correct ? | 5 Yes | 2 No |
where does 22kv line starts
we all know that in transformer, voltage and current are inversely related i.e. Vp/Vs= Is/Ip....so in standard CT..we have a ratio of 200/5...that means our voltage should increase by ratio of 40..althoug that is not the case...because that requires high insulation level.and pratically not feasible......can anybody clarify my ques.......thanx
what is the advantage of DC Motor over AC motor & Where its applicable ?
In CTs tan delta point should be earthed , what is the reason behind it?
What is error of a measurement?
can I connect step down transformer(25KvA,240V Phase to phase)to output of online UPS(15KvA,440V PHASE TO PHASE) Load connect to TRANSFORMER is 13KvA,240V PHASE TO PHASE. please brief if it is wrong
WHAT DRESS I SHOULD WEAR WHILE ATTENDING AN INTERVIEW? PLEASE SPECIFY THE STYLE AND COLOUR. CAN A LADY WEAR CHUDIDAR FOR AN INTERVIEW?
In constant power region of 3-phase IM torque-speed characteristics, if frequency increases slip A does not alter B decreases C increases D none of above
in our transmisison sub station why we step down firstly 132kv\33kv then 33kv to 11kv. can we direct step down 132kv to 11kv.
15 suspects are rounded by the police and questioned about a bank robbery. Only one of them is guilty. The suspects are made to stand in a line and each person declares that the person next to him on his right is guilty. The rightmost person is not questioned. Which of the following possibilities are true? A. All the suspects are lying. B. The leftmost suspect is guilty. B only
what is difference between earth and ground?/
3 Answers Sree Rayalseema Green Energy Limited SRGEL,
what is the effect of un-synchronized power.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)