How CT & PT ratings are decided for a 11KV or 33KV
transmission line?
Answers were Sorted based on User's Feedback
Answer / balasubramanian
CT PT ratings are decided on
1. Class : Protection, metering (for CT)
2. Burden: The load of relays, cabling, etc.
3. Fault level: The thermal capacity of CT for bearing the
fault current for required time 1 sec, 3 sec etc.
4. The voltage level of the system
| Is This Answer Correct ? | 19 Yes | 1 No |
Answer / pradeep kumar
ct decied as per metering OR protection ct Use ct as per
metering that we can use the metering instrument of panel
OR control room 1A OR 5A
| Is This Answer Correct ? | 13 Yes | 4 No |
Answer / d.durga prasad
In CT
CT primary rating will be decided by its load current &
secondary will depend up on purpose of of selection (either
metering or protection )
In PT
It will always depend upon its system rating & in secondary
the class will be depend upon its purpose of its
utilization as same as in the CT secodary. but the voltage
level is always 110V in secondary of transformer.
| Is This Answer Correct ? | 5 Yes | 2 No |
which protection function should measure RMS value of current&DFT value of current?
Why have to use copper cable for local isolator to motor ?
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
placement paper samples of mspl company
how to calculate voltage drop and followed by cable calculation?is there avail in formula?
For the requirement of a furnace of temperature range up to 1200 oC using silicon carbide rods, What is the required rate of transformer needed (please do it with all details)?
how to size H.T & L.T Panel ?
Why does increasing the magnetic flux in the main field of a d.c motor cause the armature current to reduce??
what is the working principle of DC generator ?
explain in detail HV & LV bushing connection in power transformer (110 / 11 kv 16 MVA)
6 Answers TNEB Tamil Nadu Electricity Board, wbsedcl,
How could i check the earth connection of my home using a multimeter?????? If it is possible plz help me....
why 3 phase induction motor only need starter ? why not other motors need starter ?(like synchronous motor,single phase induction motors & their types) ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)