How CT & PT ratings are decided for a 11KV or 33KV
transmission line?

Answer Posted / balasubramanian

CT PT ratings are decided on
1. Class : Protection, metering (for CT)
2. Burden: The load of relays, cabling, etc.
3. Fault level: The thermal capacity of CT for bearing the
fault current for required time 1 sec, 3 sec etc.
4. The voltage level of the system

Is This Answer Correct ?    19 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is the difference between b c d curves on mcb

1348


is oil viscosity affect on motor current?

1522


how the works electronic energy meter?

1676


sent to a site and asked to explain how you would like a twenty seven flour building should be supplied with lighting and sockets plus a water boiler.

1499


what is cause of static electricity? I experience shock when i touch metal equipment in a room ,furher check shows earth leakage showing 80ma at the DB near to the 400 MCCB?

1470






Explain few advantages of electric traction system?

600


What is effect of over voltage and under voltage on ACB

1410


Whether it is possible to measure energy at the input of rectifier transformer (12 pulse with very high odd harmonics)

1478


Write down the name of 2 lady Bir Pratin of Bangladesh

1486


Is it possible to measure correct value of earth resistance & cable insulation ristance with out disconncting earth lead & both sides of cable ends? If not, any other method to measure ER & CIR with out disconneting from the system.

1664


what is the practical application of full adder circuit?

1430


Bimetal strip used in overload relay what is that,which types of material used for that & percentage.

1798


What is meant by bus bar protection?

655


How to select a contactor? How many types of contactors are available

2745


can we use trip light with bus coupler?

1455