Electrical Design specifications
Answer / me
Greetings all,
iam working in an out door lighting design for our plant
and i calculated the total watt needed (sum of all lights)
= 53 kw, 220 volt
our power supply is 480V
so, I chosed a 75 KVA transformer dry type 480/220-127 V 3
phase 60 Hz
cable size from feeder to transformer primary = 50 mm2 (1/0
AWG)
cable size from transformer secondary to distribution panel
board = 125 mm2 (250 MCM)
distribution panel board main breacker = 250 A
So, are my calculations ok ? any changes or suggestions ?
thanks in advance
| Is This Answer Correct ? | 2 Yes | 0 No |
Why more than 2.5 MVA distribution transformers (secondary is 440V)are not used in india.
kindly tell me how the load on generator increase by just increasing the fuel of prime mover, as if for exampple 20 MW gen set is synchronized the load ramps from zero to 20 MW gradully and during this procress only fuel of prime mover increases. Which thing determines the load on generator with respect to fuel
BRIEFLY EXPLAIN THE STORAGE CLASSES AND THEIR TYPES IN C
How do you convert the lt amps on a transformer to the ht amps?
What are the factor to be consider for CT selection in 132kV substation?
we have 400kv/6.6kv transformer ,it has total 9 taps on HV side with normal tap on tap no 5.when we took the ratio test we observed that ratio was decreasing from tap 1 to tap 5 and was found increasing from tap 5 to tap 9.What is the reason?if anyone have related document then please send me on the email id ankushbahale@gmail.com......plz plz
how step up transformer step up the voltage and what is the reason behind it?
How to put breaker in service / test position.
why induction motor speed is decress with increase in load? how synchronous motor speed is constant?
long form of CT
3 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
we have two generators different capacity on 15 MW and other 6MW at 11 KV , 15 MW gen. bus short level current 40KA,and 6MW short level current 25KA,, length of cable 100MTR between 6 MW from 15MW gen. for bus coupling . kindly tell any one can we use both NGR OR one NGR from any GEN. BOTH NGR has diff. rating. Tariq pakistan
my UPS suddenly goes off and all panel light also blow off.This happens even main electric supply is not interrupted.After some time it automatically starts functioning normally.Batteries are new.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)