Electrical Design specifications
Answer / me
Greetings all,
iam working in an out door lighting design for our plant
and i calculated the total watt needed (sum of all lights)
= 53 kw, 220 volt
our power supply is 480V
so, I chosed a 75 KVA transformer dry type 480/220-127 V 3
phase 60 Hz
cable size from feeder to transformer primary = 50 mm2 (1/0
AWG)
cable size from transformer secondary to distribution panel
board = 125 mm2 (250 MCM)
distribution panel board main breacker = 250 A
So, are my calculations ok ? any changes or suggestions ?
thanks in advance
| Is This Answer Correct ? | 2 Yes | 0 No |
What is the Difference Between MCCB & ACB & VCB
what is the difference between LATCH and FLIP FLOP
what is the difference between induction and synchronous motor?explain in simple words?why 3 phase motor is given preference over single phase motor.
formula for calculation of switchgears(i.e. contactor, fuse, cb, relay etc.), if load current is given?
freuency meter
Why distribution transformer secondary voltage is 0.433kV instead of 0.415kV.all other switchgear rating are 415 volt??
what is the relation between Sq mm of wire and its current carrying capacity?
what is meant by phase transformation ratio in induction motors?
Is only insulation the difference between High voltage and Medium voltage cable?
Why Phase to Neutral get spark
calculation of knee point voltage of current transformer?
What are the solutions for avioding sulfide formation at bimetalic (Copper &Aluminium)overhead joints?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)