Electrical Design specifications
Answer / me
Greetings all,
iam working in an out door lighting design for our plant
and i calculated the total watt needed (sum of all lights)
= 53 kw, 220 volt
our power supply is 480V
so, I chosed a 75 KVA transformer dry type 480/220-127 V 3
phase 60 Hz
cable size from feeder to transformer primary = 50 mm2 (1/0
AWG)
cable size from transformer secondary to distribution panel
board = 125 mm2 (250 MCM)
distribution panel board main breacker = 250 A
So, are my calculations ok ? any changes or suggestions ?
thanks in advance
| Is This Answer Correct ? | 2 Yes | 0 No |
Is it mandatory statutory requirement of transformer oil filtration annualy despite oil is withstanding required dieelectrical strenth and all others parameters
what is hormonics. how it is generated & what are the problem faced by that.
what is the working principle of three point starter of dc motor?
1 Answers Ashok Leyland, Cap Gemini, Infosys, Just Dial,
2 Diesel Generators 900KVA connected to the bus bar for essential load as an alternative for power taken from 11/440V 3KVA Transformer supplying this bus bar. my question here is in the event of power failure on 11KV side can I feed the power to 11 KV bus by using the same transformer as reverse feed, what will be the inrush current???
For 7.5kw star delta starter how to calculate 1. Mccb rating 2. Contactor rating 3. Over load relay rating
which connection is safer series or parallel?usually which connection we prefer at home?
how can we say that stator magnetic field rotates with synchronous speed?can we derive?
How many no. of earthing pits required for commisioning a new 320KVC DG Set????How????
how to decide the ratings of the busbar in electrification.give me the proper thumb rule or procedure
Mention what are the different colors on wires indicates?
In a large office how do we calculate required number of light fittings, assuming fittings are 4x18W or 2x36W fluorescent fitting ?
WHEN SINGLE PHASE SUPPLY AS 220V, WHY THE 3 PHASE- 4 WIRE MEASURED AS 440 VOLTS INSTEAD OF 660 VOLTS (220 VOLTS PER PHASE i.e 220x3 = 660 volts ).
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)