2 Diesel Generators 900KVA connected to the bus bar for
essential load as an alternative for power taken from
11/440V 3KVA Transformer supplying this bus bar. my
question here is in the event of power failure on 11KV side
can I feed the power to 11 KV bus by using the same
transformer as reverse feed, what will be the inrush
current???
Answers were Sorted based on User's Feedback
Answer / joy
Your generator will be damaged. The reason being
that the transformer impedance as well as
impedeance of the entire 11kv side will be loaded
on the generator. Besides the inrush current which
the transformer will take when you charge it. This
will lead to the dropping of pf of the generator,
leading to the heating of its windings. Also you
have to make sure there are no chances of the
"normal" 11kv source being re applied when the
generator is being used to charge the 11kv side. Or
else the generator will experience a shearing of
its rotor.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / a. magesh kumar
My understanding is two 900 KVA generator, alternatively
feeds the supply to transformer (one at a time), the
transformer step down voltage 11KV/ 400V (3KVA). This 440V
feeds to connected load (seconday side of the transformer).
Ur question: In the event of Power failure 11KV side
(primary), what will be the inrush current?
whether u r asking short circuit current or else?
Inrush rush Current:
AC power may happen to be applied to the primary winding of
a power transformer at any point in the voltage cycle.
Excessive current inrush can result if the primary voltage
suddenly goes from zero to a high value rather than
increasing sinusoidally as it does during normal operation.
Excessive inrush current to a large transformer may not
only blow a fuse, trip a breaker, cause a sharp dip in
mains voltage, damage transformer windings, or damage
electrical supply circuits, it also induces a very large
voltage spike in the transformer secondary winding. Large
secondary voltage spikes can breakdown winding insulation,
damage rectifiers, and damage other power supply components
When switching power supplies are first turned on, they
present high initial currents as a result of filter
capacitor impedance. These large filter capacitors act like
a short circuit, producing an immediate inrush surge
current with a fast rise time. The peak inrush current is
several orders of magnitude greater than the circuit's
steady state current. This power surge can seriously damage
other components
Calculate the Steady State Current:
(Available data from ur mail)
Transformer power: 3 KVA
Primary Voltage : 11 KV
Secondary Voltage : 415 V
Efficiency : 85 % (assumed)
Impedance : 4 % (assumed)
Steady State Current: (KVA of transformer) / (efficiency
of transformer) X (Minimum Input voltage)
: 3 KVA / (0.70) X (415)
: 10.32 Amps.
Short Circuit Calculation: 3 KVA / 415
: 7.2 A
: 7.2 * 25 (impedance)
: 180.7 A (0.18 KA)
Short circuit current is 187.5 Amps.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / harsh
first answer is correct.
the generator will never damage while giving reverse
feedback.
its only to chack whether is there any fault in our cables
or any other machinery or furnaces.
| Is This Answer Correct ? | 3 Yes | 1 No |
what happen when ac motor is connected with dc current
Draw a SLD for main panel for school having connected load of 1200kw and emergency generator 200kw.also show the increase of additional load of chiller 225kw in the lv panel indicating meter postion size of transformer ,cables and capacitor bank.
How they LT panel busbar size choose
What is evaporator & condencer & compressor
which types of relay used in acb and vcb?
what is the range of maximum DOL and SDS can be use for pump and fan application
how the magnetic flux is said to be rotating & alternating?
can i connect REF and Differencial relay in 1 CT core for transformer protection?
What is the difference between amorphous core transformer and CRGO core transformer?.
what about the input current fan when regulator regulates to speed low?
what is the principal of braker
How we find the size of cable if we know the current
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)