For 7.5kw star delta starter how to calculate
1. Mccb rating
2. Contactor rating
3. Over load relay rating
Answer / joeredd
You need to know the full load motor current at the supply voltage you are going to be using. Your contactors/overload are rated on current. Their voltage rating needs to be higher than the supply voltage. (I.e. 415vac supply, 600vac rating). Knowing the motor wattage (7.5Kw) on its own is not helpful.
| Is This Answer Correct ? | 3 Yes | 0 No |
Can VFD step up to 60 Hz if it is designed to receive 50 Hz input?
for compensate 315mh inductance ,how many capaciance required?
suppose we using 3 phase motor of 440 v means what range of C.T. is require for measuring current ?
where the protection CT in neutral of transformer be located, before bifurcation or after bifurcation and why.
what happen when power factor of 2 parallely operated transformer become equle?
how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula
Hi, i want to know is meant by power quality? How it can calculated ? How we can improve?
In both 600/1000 V cable and 450/750 V cable, we can supply 415 V. However for distribution, all utilities are using only 600/100 V instead of 450/750 V. What is the reason?
What is application of MCB & How it works
Could explain briefly of over excitation in transformer.
what is iron loss?
1. what is difference between VCB and ACB.how its works please explian.
6 Answers ABB, Accenture, HP, Minda, Mother Dairy, Satyam Pharma,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)