For 7.5kw star delta starter how to calculate
1. Mccb rating
2. Contactor rating
3. Over load relay rating
Answer / joeredd
You need to know the full load motor current at the supply voltage you are going to be using. Your contactors/overload are rated on current. Their voltage rating needs to be higher than the supply voltage. (I.e. 415vac supply, 600vac rating). Knowing the motor wattage (7.5Kw) on its own is not helpful.
| Is This Answer Correct ? | 3 Yes | 0 No |
what is power factor? is it good or bad for a system? what will happen if power factor increase or decrease?
how we are measuring the winding temperature of the transformer?
type of transformer
why we need the starters for motors
TNC switch is also available in 1NO+1NC. What does it mean ?
What is SFU why it is used
why air handling unit interloking in case of fire
State thevenintheorem?
What will happen if we give the 3 phase supply to the rotor of slipring induction motor?
A 12.5 hp slip ring motor taking high initial current and its MPCB is getting open.what may be the reason?
can you show me the components inside a air circuit breaker with connection diagram?
How many types of isolator is available for H.T.lines? which one is best for sub-station?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)