Answer / iamdon
CT is used mainly for Instrumentation(Measurement and
protection system) purposes thats why it is also termed as
instrument transformer.The measuring and protecting devices
are not rated to sustain high currents.What a CT does is,
it lowers the current in secondary side so that measurement
as well protection can be done at a reduced level of
current.
The digit in CT ratio of secondary side is IS standard for
rated secondary current so that uniformity among manufactures
be established.
The various values of secondary currents are
1)in the range of 0-5 amp e.g, 1A,5A
2)in the order of mA(particularly 40mA)in case of digital
devices for measurements and protection.
Perhaps Shayam had ingnored this fact.It cann't be any
number.
Author:arbelectbit@yahoo.com
Is This Answer Correct ? | 15 Yes | 2 No |
Answer / nagesh
the first part will show the primary current eg 75/5 75 amp
will be your primary current and 5amp represents the
secondary current, but its not always 5, even in market
30/1 and 50/1 etc is also avaiable, but true there is an
standard. Rest all what Iamdon said perfectly ok.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / k.prakashchandra
Secondary 5 A was used earlier.Now with electronic relays
and meters ,the secondary is 1 A
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vinod g
Purpose of INSTRUMENT TRANSFORMER (CT & PT) is to reduce
the voltage and current respectievly.In EHV/HV/MV voltage
and current for the protection/metering canot be taken
directly as its voltage is very high and required huge
insulation and cost, so PT & CT is using to stepdown
voltage and current. Protection CT and measuring CT are
different class of manufaturing and secondary current
normally one amps but it can be manufactured as per
customer requirement. in 415 V also CT is using if current
is high.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / dipak
ct secondary current is always 1 or 5 amp . i think 1 amp where the current path is short and less relay are installed. and where the current path is long it is 5 amp to avoid loading.
Is This Answer Correct ? | 0 Yes | 3 No |
Answer / shyam
hear 5 is primary winding turns of the CT .it can be any
number not only 5
Is This Answer Correct ? | 3 Yes | 14 No |
In a star(primary) to delta(secondary) transformer,how you take the neutral point?
What is the difference between single point and double point bonding. please kindly detail about bonding of cables.
why and where we use early make & late break contacts in protection?
why should series motor be started with load and shunt motor should be started without load??????
Explain and give me an example of a time when you had to explain some new procedures to your co-workers for quality service delivery, how did you go about it?
In case of generator when we consume more power produces by it why load on generator increase and starts sound more. and how it is adjusted..
how power saving takes place through VFD?
Write down the name of 2 lady Bir Pratin of Bangladesh
how the testing of CT OF 400/200/100 done in33/11 kv s/s
Does all the output contacts (N/O as well as N/C) of a Numerical relay operate when relay receives a binary input/inputs or contacts are designated to specific logic input/inputs and only these contacts operate?
Why in medium voltage system(3.3kv to 33kv, neutral is earthed with either resistance, reactance or neutral grounding resistance?
can a 150 kva 3 phase 440v/230V delta-wye step down transformer can be use as step up transfoermer with connected loads at 440v side?