why the CT ratio secondary is always divided by 5 for eg( 75/5,80/5,50/5)..

Answer / iamdon

CT is used mainly for Instrumentation(Measurement and
protection system) purposes thats why it is also termed as
instrument transformer.The measuring and protecting devices
are not rated to sustain high currents.What a CT does is,
it lowers the current in secondary side so that measurement
as well protection can be done at a reduced level of
current.

The digit in CT ratio of secondary side is IS standard for
rated secondary current so that uniformity among manufactures
be established.
The various values of secondary currents are
1)in the range of 0-5 amp e.g, 1A,5A
2)in the order of mA(particularly 40mA)in case of digital
devices for measurements and protection.


Perhaps Shayam had ingnored this fact.It cann't be any
number.

Author:arbelectbit@yahoo.com

Is This Answer Correct ?    15 Yes 2 No

why the CT ratio secondary is always divided by 5 for eg( 75/5,80/5,50/5)..

Answer / nagesh

the first part will show the primary current eg 75/5 75 amp
will be your primary current and 5amp represents the
secondary current, but its not always 5, even in market
30/1 and 50/1 etc is also avaiable, but true there is an
standard. Rest all what Iamdon said perfectly ok.

Is This Answer Correct ?    3 Yes 1 No

why the CT ratio secondary is always divided by 5 for eg( 75/5,80/5,50/5)..

Answer / k.prakashchandra

Secondary 5 A was used earlier.Now with electronic relays
and meters ,the secondary is 1 A

Is This Answer Correct ?    0 Yes 1 No

why the CT ratio secondary is always divided by 5 for eg( 75/5,80/5,50/5)..

Answer / vinod g

Purpose of INSTRUMENT TRANSFORMER (CT & PT) is to reduce
the voltage and current respectievly.In EHV/HV/MV voltage
and current for the protection/metering canot be taken
directly as its voltage is very high and required huge
insulation and cost, so PT & CT is using to stepdown
voltage and current. Protection CT and measuring CT are
different class of manufaturing and secondary current
normally one amps but it can be manufactured as per
customer requirement. in 415 V also CT is using if current
is high.

Is This Answer Correct ?    0 Yes 1 No

why the CT ratio secondary is always divided by 5 for eg( 75/5,80/5,50/5)..

Answer / dipak

ct secondary current is always 1 or 5 amp . i think 1 amp where the current path is short and less relay are installed. and where the current path is long it is 5 amp to avoid loading.

Is This Answer Correct ?    0 Yes 3 No

why the CT ratio secondary is always divided by 5 for eg( 75/5,80/5,50/5)..

Answer / shyam

hear 5 is primary winding turns of the CT .it can be any
number not only 5

Is This Answer Correct ?    3 Yes 14 No

Post New Answer

More Electrical Engineering Interview Questions

In a star(primary) to delta(secondary) transformer,how you take the neutral point?

3 Answers   HLL,


What is the difference between single point and double point bonding. please kindly detail about bonding of cables.

0 Answers  


why and where we use early make & late break contacts in protection?

0 Answers  


why should series motor be started with load and shunt motor should be started without load??????

7 Answers  


Explain and give me an example of a time when you had to explain some new procedures to your co-workers for quality service delivery, how did you go about it?

0 Answers  






In case of generator when we consume more power produces by it why load on generator increase and starts sound more. and how it is adjusted..

0 Answers  


how power saving takes place through VFD?

9 Answers  


Write down the name of 2 lady Bir Pratin of Bangladesh

0 Answers  


how the testing of CT OF 400/200/100 done in33/11 kv s/s

1 Answers   Reliance,


Does all the output contacts (N/O as well as N/C) of a Numerical relay operate when relay receives a binary input/inputs or contacts are designated to specific logic input/inputs and only these contacts operate?

0 Answers  


Why in medium voltage system(3.3kv to 33kv, neutral is earthed with either resistance, reactance or neutral grounding resistance?

4 Answers   Essar,


can a 150 kva 3 phase 440v/230V delta-wye step down transformer can be use as step up transfoermer with connected loads at 440v side?

0 Answers   RD Square,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)