why the CT ratio secondary is always divided by 5 for eg(
75/5,80/5,50/5)
Answers were Sorted based on User's Feedback
Answer / iamdon
CT is used mainly for Instrumentation(Measurement and
protection system) purposes thats why it is also termed as
instrument transformer.The measuring and protecting devices
are not rated to sustain high currents.What a CT does is,
it lowers the current in secondary side so that measurement
as well protection can be done at a reduced level of
current.
The digit in CT ratio of secondary side is IS standard for
rated secondary current so that uniformity among manufactures
be established.
The various values of secondary currents are
1)in the range of 0-5 amp e.g, 1A,5A
2)in the order of mA(particularly 40mA)in case of digital
devices for measurements and protection.
Perhaps Shayam had ingnored this fact.It cann't be any
number.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 15 Yes | 2 No |
Answer / nagesh
the first part will show the primary current eg 75/5 75 amp
will be your primary current and 5amp represents the
secondary current, but its not always 5, even in market
30/1 and 50/1 etc is also avaiable, but true there is an
standard. Rest all what Iamdon said perfectly ok.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / k.prakashchandra
Secondary 5 A was used earlier.Now with electronic relays
and meters ,the secondary is 1 A
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vinod g
Purpose of INSTRUMENT TRANSFORMER (CT & PT) is to reduce
the voltage and current respectievly.In EHV/HV/MV voltage
and current for the protection/metering canot be taken
directly as its voltage is very high and required huge
insulation and cost, so PT & CT is using to stepdown
voltage and current. Protection CT and measuring CT are
different class of manufaturing and secondary current
normally one amps but it can be manufactured as per
customer requirement. in 415 V also CT is using if current
is high.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / dipak
ct secondary current is always 1 or 5 amp . i think 1 amp where the current path is short and less relay are installed. and where the current path is long it is 5 amp to avoid loading.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / shyam
hear 5 is primary winding turns of the CT .it can be any
number not only 5
| Is This Answer Correct ? | 3 Yes | 14 No |
difference between the applicability of nortons and thevenin theorem
why we are having many type of vector group in the transformer ,what is the use of it?
How we calculate the size of ht cable for any transformer
What is the drawback of class b amplifier?
HOW TO CALCULATE GROUND FAULT CURRENT IN 430V 4000AMP AIR CIRCUIT BREAKER?
What is the percentage loss for aluminium wire for HT line more than 11KVa
how "rabbit ACSR" conductors are more efficient than "weasel ACSR" conductors
What is the de rating factor of cable? What is the importance of the de rating factor in cable selection?
what is the star delta connetion and how can do it a three phase motor with control witing with picture
0 Answers Aurobindo, SA Kent, Wipro,
If there is volagte between earth and neutral, what should be the reason ? and solution * What should be allowable limit in case, if the voltage between earth and neutral exist ? / OR what is limit for safe voltage between earth and neutral?
What is DC power factor??
How do ACB are maintenance, what are the problem occurred in ACB
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)