Why star point of star connected motor is not grounded?
Why alternator is operated at lagging power factor?
Answers were Sorted based on User's Feedback
Answer / leo felix.d
The transfromer's secondary which is feeding 3 phase motor
is already earthed.so there is no need to earthe the motors
star point again. Because earth resistance wont be same
every where.If we eartherd both the ends,there will be a
current flow between two neutrals.
universaly,in industries 70% of loads are inductive tupr
which are having lagging PF nature.Always load only decides
the power factor not source(Alternator).So that only the
rating always mentioned as VA and not watts.
Is This Answer Correct ? | 30 Yes | 5 No |
Answer / avinash
3 phase star connected motor no need to grouned neutral
because mostly load current is balanced. But 6.6 KV y
connected motor has provided neutral c.t. for protection
purpose. so grounded neutral is providing in HT MOTOR.
Is This Answer Correct ? | 3 Yes | 7 No |
Answer / santosh kawade
3 phase motor is a balance load, hence we are not require
to connect star point of star connected motor to ground.
Due to balance load there will not be any current flow from
neutral and connecting star point create unnecessary
wastage of material and money.
santosh kawade
Is This Answer Correct ? | 3 Yes | 17 No |
If a earth leakage circuit breaker trips is it possible to tell which house circuit breaker (I have four) is the faulty circuit?
In between UPS out going changer over switch and ups raising main input, both side cable gland producing heat but the cable doesn't get heat,Why?
sometime battery charged and then automatically charged when rectifier ON conition, is there any chances please clarify the same.
On monitor it is written that current rating is 2.2 Amps. Is it a monitor current drawing capacity or CPU & monitor. If it is only monitor rating, what will be the rating of only CPU and what will be the power consumption rating of PC, Monitor & Scanner? In net, I learnt that computer consumes only 200-300W while running. With the current rating of 2.2 Amps, how it could be 200-300Watts. Please explain?
i am using star-delta connections with reverse/forward direction motion of the 75hp induction motor.What should be the ratings of Main,Delta and Star contactors and why?
What is the function of electron gun used in crt?
what condition there autotransformer will fail?
what is the formula to find out how many amps generater takes running on full load.
ful form of gis
How to calculate the input cable rating for 10kva ups (3phase input and single phase output and also 3phase output, battery rating 65Ah)provide the formula also.thnx
How to calculate the value of earth capacitance in a transmission line.
WHY AIR COMPRESOR IS STARTED UNLOADED