how to calculate the kw, Amps consumed by a capacitor,
give me the formula for KVAr into capacitance,KVAr into KW
& KVA, Amps
Answers were Sorted based on User's Feedback
Answer / pugalenthi.s
Amps can be calculated by = KVAr / (V line to line * 1.732
for three phase.
KW can be calculated by = V * I * 1.732
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / michael
Amp consume by the capacitor simply Q = VIrf
where rf = sin theta, since it is
capacitor so theta = 90 deg
sin 90 = 1
so simple I = Q/V
Q = reactive power
V = voltage
I = current
(KVA)^2 = KW^2 + KVAR^2
since purely capacitiy KW = 0
therefore KVA = KVAR..
NOTE : in a purely capacitive or inductive
real power always Zero
| Is This Answer Correct ? | 2 Yes | 0 No |
what is the pressure in side transformer under normal condition?
Can someone tell me how to calculate the size of a power cable? What are the factors involved in cable sizing?
what happen if generator exitation lost?
what is difference between isolation and ultra isolation transformer?, what is the method of testing ?
Comparative difference between 33Kv & 66KV for transmitting the load of 7 MW at a distance of 34 Km.
DEAR SIR/MADAM,CLEARLY EXPLAIN ABOUT CRAWLING AND COGGING EFFECTS IN INDUCTION MOTOR.
WHY WE USE CABLE JUNCTION AFTER BETWEEN TANSMISSION LINE AND TRANSFORMER
Which are resistive loads & which one are inductive loads : Refrigerator, Split air conditioner, ceiling fans, well pump, fluoresecent bulbs, T.V, CRT Monitors, Adsl Routers, C.P.U, Printers, Deep Freezers, Speakers, DVD Players, Microwave oven etc. ? Output Power for these Appliances Would be same like this : P = V * A * P.F Or would be changed ? thanks
What is the unit of attenuation?
Grounding. Dear all at one of my site we checked the amps at the earthing cable to the alternator it was found 125 to 130 A. at the neutal cable in same machine found 146A. in the same plant checked the earthing current on other alternator it was 52A, and neutral 116 A. we are facing problems with our controller and the card was damaged once. can that neutral/GND current be a reason? as there is common grounding for the Alternator,Brkr panel,Transformer?
what is the effect of leading power factor on Power transformers in existing in major power utility
primery try cell?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)