i am working in thermal power plant .
if temperature transmitter is not showing reading in dcs
then how can we rectify the problem?

Answers were Sorted based on User's Feedback



i am working in thermal power plant . if temperature transmitter is not showing reading in dcs th..

Answer / k.sreenivasan

Go to the field and check the local indication in the
transmitter.(normally it is in either engg. units or as
percentage)
If it is zero ,then the problem is in the sensor or
terminal connection, because most of the current generation
transmitters are highly accurate and have longer stability
periods.
Suppose local reading is ok,then check the DCS analog input
card for any fault condition and clear it.Normally this
situation is rare.

Is This Answer Correct ?    24 Yes 1 No

i am working in thermal power plant . if temperature transmitter is not showing reading in dcs th..

Answer / s. kanniyappan

Check the Sensor properly. if it is ok, then
1)check continuity between the sensor cables
2)tight the cables properly
3)check the transmitter supply (24vdc)
if it is not ok, then check the DCS analog i/p cord.

Is This Answer Correct ?    14 Yes 0 No

i am working in thermal power plant . if temperature transmitter is not showing reading in dcs th..

Answer / k.manikanta naidu

check the millivolts output of thermocouple.then multiply
with the standard values depends on the type of
thermocouple.if the value is ok,check the temparature
trnsmitter,then check the mA o/p of TT.

Is This Answer Correct ?    8 Yes 0 No

i am working in thermal power plant . if temperature transmitter is not showing reading in dcs th..

Answer / g kiran kumar

1. Check the wiring at all terminal blocks at field, at
control panel and at PLC for any loose connection.
2. Check the Transmitter supply.
3. Measure the output from Transmitter.
4. Check cable continuity.
5. Finally check the configuration of TAG in the DCS (may
be someone deleated accidently).

Is This Answer Correct ?    6 Yes 0 No

i am working in thermal power plant . if temperature transmitter is not showing reading in dcs th..

Answer / satish

SEE THE FIRST ALRM CONDITION ON TRANSMITTER BECAUSE MOST
PROBABILITY IN PRIMERY ELEMENT PROBLE.

Is This Answer Correct ?    6 Yes 3 No

i am working in thermal power plant . if temperature transmitter is not showing reading in dcs th..

Answer / pradeep kumar

check the tt reading once again check the main cable (from
element resistance or mv)and also check the branch
cable(from dcs 24 v)its available the problem in dcs side
check the analog modules

Is This Answer Correct ?    1 Yes 0 No

i am working in thermal power plant . if temperature transmitter is not showing reading in dcs th..

Answer / altamash

first check the TB in marshalling cabinet then check local display in transmitter and then DCS

Is This Answer Correct ?    0 Yes 0 No

i am working in thermal power plant . if temperature transmitter is not showing reading in dcs th..

Answer / srinivas

check wiring in i/o

Is This Answer Correct ?    1 Yes 5 No

Post New Answer

More Instrumentation Interview Questions

how to convert % to ma

1 Answers   Flour Tech Engineers (P) Ltd, Techint,


What is the calibration procedure of Drum level transmitter if range is 0 to -400 mmh2o in lab?

0 Answers  


what is function of SCADA , and how is it work, explain with difination

0 Answers   Bapco Bahrain Petroleum Company,


i want all model questions paper for robert bosch

1 Answers   Bosch, Patni,


Close loop and open loop diagram for instrumentation

1 Answers   Petron ltd,






Specify eight technical requirements that you would consider important, when deciding upon a particular control valve?

0 Answers  


what do you mean by cathodic protection?

1 Answers   Saipem,


What is the difference between uv and ir scanners? and what is the workig principle of both

0 Answers  


please send the drdo exam paper

0 Answers   DRDO,


What is the difference between EPROM & EEPROM.

1 Answers   Sabic,


Sitrans LR460 Radar level transmitter getting level out or disturbed level during moisture present in the material ie coal in the pccb bunker in CHP.Any suggestions for this problem...????

1 Answers   ABG Shipyard,


Calibration procedure for Electro magnetic Flow meter

0 Answers   Reliance,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)