i am working in thermal power plant .
if temperature transmitter is not showing reading in dcs
then how can we rectify the problem?
Answers were Sorted based on User's Feedback
Answer / k.sreenivasan
Go to the field and check the local indication in the
transmitter.(normally it is in either engg. units or as
percentage)
If it is zero ,then the problem is in the sensor or
terminal connection, because most of the current generation
transmitters are highly accurate and have longer stability
periods.
Suppose local reading is ok,then check the DCS analog input
card for any fault condition and clear it.Normally this
situation is rare.
| Is This Answer Correct ? | 24 Yes | 1 No |
Answer / s. kanniyappan
Check the Sensor properly. if it is ok, then
1)check continuity between the sensor cables
2)tight the cables properly
3)check the transmitter supply (24vdc)
if it is not ok, then check the DCS analog i/p cord.
| Is This Answer Correct ? | 14 Yes | 0 No |
Answer / k.manikanta naidu
check the millivolts output of thermocouple.then multiply
with the standard values depends on the type of
thermocouple.if the value is ok,check the temparature
trnsmitter,then check the mA o/p of TT.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / g kiran kumar
1. Check the wiring at all terminal blocks at field, at
control panel and at PLC for any loose connection.
2. Check the Transmitter supply.
3. Measure the output from Transmitter.
4. Check cable continuity.
5. Finally check the configuration of TAG in the DCS (may
be someone deleated accidently).
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / satish
SEE THE FIRST ALRM CONDITION ON TRANSMITTER BECAUSE MOST
PROBABILITY IN PRIMERY ELEMENT PROBLE.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / pradeep kumar
check the tt reading once again check the main cable (from
element resistance or mv)and also check the branch
cable(from dcs 24 v)its available the problem in dcs side
check the analog modules
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the difference between signal cable and ontrol cable?
what is load line in control valve?
3 Answers Boral, Qatar Petroleums,
What means zero and span in transmitter callibration.
If an Instrument has 550 ohm internal resistance and the cable used for that instrument is 0.5 ohm per meter resistance. If the voltage is 12volt.How much length cable can be used?
Boiler flame scanner working principle?
How can we test a bently nevda 3500/42M accelerometer monitor card by simulating it with test equipment?. what king od of signal (milli volts or volts or or resistance ) we should feed in the terminals of the card?
what is Green field /brown field exposure in chemicals /oil /petrochemicals /refineries /paints /speciality chemicals /gas /FMCG /glass industry
Please can anybody tell me the step by step procedure for calibrating the Pr,Lvl,Fl,Temp transmitter on process?
how we can calibrate level transmiiter in field?
what is the use of conrol cable..?
How to calibration coriolis flow meter?
The Design Calculation of Level Transmitter For Different Structure open & Closed Vessel, Eg. Diff. Level Tx., Capacitance For Continous Operation
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)