Answer / n.venkidusamy
I think that site tests.ie. Pre commissioning Tests of
following.
1. Insulation Resistance Test for breaker and protection
and other cables
2. Check for spirit level
3. Mechanical spring charge test
4. Mechanical ON/OFF test
5. Electrical spring charge test
6. Electrica ON/OFF Both Local and remote Test
7. Contact resistance Test
8. opening and Closing timings tests.
9. Protection trip Test
10. Check for operation of Closing coil at 80% and Trip
coil at 70% rated Control D.C.voltage
Is This Answer Correct ? | 14 Yes | 0 No |
I belive you mean commisioning tests.
some of them are,
A)INSULATION TEST
b)contact resistance test
c)HV holding test
d)primary and sec injection test on the protection cct
e)transformers insulation, ratio test,vector group, insulating
oils dielectric tests.
f)cables insulation, phasing test
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / mriganka das
Transformer:
1)IR Test
2)Magnetising Current Test
3)Magnetic Core Balance Test
4)Vector Group Test
5)Ratio Test
6)Polarity Test
7)Oil Test (DGA,Dielectric Strength,Moisture content)
8)RLA test (Dirana, Thuran)
Current Transformer :
1) Ratio Test
2) IR Value Tset
3) Polarity Test
4) Knee Voltage Check
5) Winding Resistance Test
6) Back to Back Test
7) Tan Delta Test
8) High Voltage Test
Breacker Test:
1) IR Value Tset
2) Contact Resistance Test
3) Closing Tripping Timing Test
4) High Voltage Test
Isolator Test:
1) IR Value Tset
2) Contact Resistance Test
3) Closing Tripping Timing Test
4) High Voltage Test
5) Hot point Check ( in running condition)
Is This Answer Correct ? | 7 Yes | 1 No |
what will happen when a electric bulb is connected between two phases.it will glow or not
how to measure genset CT coil range?
What is the Operating Powerfactor of UPS??? Why??
what are the different types of transformers in present? which transformer is efficient?
what is over frequency protection
if earthing is not connected to computers any problem ?
Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups ac supply only.
12 Answers ACC, JLL, ZETDC,
WHY DISEL GENRATOR SET SHUT DOWN IN OVER LOAD CONDITIONS
i have 28/32 MVA power transformer with 11/6.6 KC voltage rating and 12%impedance.it have star connection at both side.but it have another thied winding tertiary winding.what is used of this winding. pl tell me
What is UPS and How do you maintain the UPS Maintenance? Brief Description on UPS maintenance.
0 Answers JLL, Nokia, Uttam Galva,
What is creepage distance..... what will be the value for different voltage level
Efficient electrical earthing in hard rock area