What types of testing in 11Kv Ht switchgeat during testing?
Answers were Sorted based on User's Feedback
Answer / n.venkidusamy
I think that site tests.ie. Pre commissioning Tests of
following.
1. Insulation Resistance Test for breaker and protection
and other cables
2. Check for spirit level
3. Mechanical spring charge test
4. Mechanical ON/OFF test
5. Electrical spring charge test
6. Electrica ON/OFF Both Local and remote Test
7. Contact resistance Test
8. opening and Closing timings tests.
9. Protection trip Test
10. Check for operation of Closing coil at 80% and Trip
coil at 70% rated Control D.C.voltage
Is This Answer Correct ? | 14 Yes | 0 No |
I belive you mean commisioning tests.
some of them are,
A)INSULATION TEST
b)contact resistance test
c)HV holding test
d)primary and sec injection test on the protection cct
e)transformers insulation, ratio test,vector group, insulating
oils dielectric tests.
f)cables insulation, phasing test
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / mriganka das
Transformer:
1)IR Test
2)Magnetising Current Test
3)Magnetic Core Balance Test
4)Vector Group Test
5)Ratio Test
6)Polarity Test
7)Oil Test (DGA,Dielectric Strength,Moisture content)
8)RLA test (Dirana, Thuran)
Current Transformer :
1) Ratio Test
2) IR Value Tset
3) Polarity Test
4) Knee Voltage Check
5) Winding Resistance Test
6) Back to Back Test
7) Tan Delta Test
8) High Voltage Test
Breacker Test:
1) IR Value Tset
2) Contact Resistance Test
3) Closing Tripping Timing Test
4) High Voltage Test
Isolator Test:
1) IR Value Tset
2) Contact Resistance Test
3) Closing Tripping Timing Test
4) High Voltage Test
5) Hot point Check ( in running condition)
Is This Answer Correct ? | 7 Yes | 1 No |
what is the difference between LPF and UPF wattmeter and where it is used.
What is best method of Calculating Short Circuit current in power system network.
Why not using Air circuit breaker at High tension side?
why neutral is required in electrical system
what are the industrail measures to over ferranti effect? how would the ferranti effect the power system if those remedial mearsure arent taken? how often does this effect occurs in real power system?
WHAT SHOULD BE THE RATING OF MCCB FOR 415V,3Ph,50KVAR CAPACITOR BANK
Induction motor & transformer both has magnetic core,then why induction motor is a inductive load & transformer not???
why we used ZNO in Lightning arrester.
How to know of any cable size if there are not written on cabl?
Name two types of electrical analogous for mechanical system.
where used of HVDS system.
How can I calculate the Mega watts required to run a plant having many electric motors and other electrical components.