What types of testing in 11Kv Ht switchgeat during testing?
Answers were Sorted based on User's Feedback
Answer / n.venkidusamy
I think that site tests.ie. Pre commissioning Tests of
following.
1. Insulation Resistance Test for breaker and protection
and other cables
2. Check for spirit level
3. Mechanical spring charge test
4. Mechanical ON/OFF test
5. Electrical spring charge test
6. Electrica ON/OFF Both Local and remote Test
7. Contact resistance Test
8. opening and Closing timings tests.
9. Protection trip Test
10. Check for operation of Closing coil at 80% and Trip
coil at 70% rated Control D.C.voltage
| Is This Answer Correct ? | 14 Yes | 0 No |
I belive you mean commisioning tests.
some of them are,
A)INSULATION TEST
b)contact resistance test
c)HV holding test
d)primary and sec injection test on the protection cct
e)transformers insulation, ratio test,vector group, insulating
oils dielectric tests.
f)cables insulation, phasing test
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / mriganka das
Transformer:
1)IR Test
2)Magnetising Current Test
3)Magnetic Core Balance Test
4)Vector Group Test
5)Ratio Test
6)Polarity Test
7)Oil Test (DGA,Dielectric Strength,Moisture content)
8)RLA test (Dirana, Thuran)
Current Transformer :
1) Ratio Test
2) IR Value Tset
3) Polarity Test
4) Knee Voltage Check
5) Winding Resistance Test
6) Back to Back Test
7) Tan Delta Test
8) High Voltage Test
Breacker Test:
1) IR Value Tset
2) Contact Resistance Test
3) Closing Tripping Timing Test
4) High Voltage Test
Isolator Test:
1) IR Value Tset
2) Contact Resistance Test
3) Closing Tripping Timing Test
4) High Voltage Test
5) Hot point Check ( in running condition)
| Is This Answer Correct ? | 7 Yes | 1 No |
how many winding in the single phase transformer?
sir, is there any ratio,this much of A.C volt is equal to D.C voltage
please let me know , we have installed two separate motor for fire fighting system 1) 60 hp and 2) 15 hp the load is 74 AMPS and 20 AMPS then tell me the main power cable in Aluminum will be what thickness , the length is 225 mt from the main utility to fire pump house
1)What will happen when 240 VDC supply is connected to 240VAC supply(DC supply +ve is connected to phase of AC supply & DC supply is to neutral of AC supply). 2)Also what will happen when 240 VDC supply is connected to 240 VAC supply in reverse polarity as of Sr. No 1.
i have interview in Pepsi company what type of question will ask please send the question and answeer
why the genearation of electricity always in form of sine wave only ??? why not cosine wave ???
What is the function of semicon in 33kv ht cable ?
Why DC current is not used in transformer?
what is vector diagram in three phase transformer
What is the material used for the core of a high freiquency transformer?
what about the power of wattmeter at starting and loding?
why rotor winding in induction motor is not earthed. normally we uses star winding in rotor .why?
3 Answers Anglo Platinum, TATA,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)